    My microwave is rated 12.7 amps and it blows the 15 amp breaker when it is on.
    If it is on for short times, there is no problem but over 2 minutes is sure to break the circuit. There are other plugs on the same circuit but they are not in use. Can I replace the breaker with a 20 amp circuit?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jun 27, 2010, 03:05 PM

    If this has just started to happen it may be the magnetron.


    You cannot put a 20A breaker on 14 AWG wire. It must be 12 awg.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Jun 27, 2010, 04:03 PM
    Most microwaves need to be on a 20 amp circuit although many are OK on a 15 amp. Anything else on that circuit?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can 20 amps breaker pull 15 amp air condition [ 3 Answers ]

My air condition says it need a 15 amp break but my breaker is 20 amp but it keeps throwing the break why is that

My compressor is rated for 19 amps, running 11.7, good or bad? [ 5 Answers ]

I just had a technician out to do a tune-up on my heat and air conditioning. He tested the amperage on my compressor, fan motor and blower motor. They were all below the rated amperage. Is that a good thing or bad? Also, does anyone know what a reasonable cost to recharge freon in a 4 ton unit...

How do I know what my generator is rated for in regards to amps ? [ 14 Answers ]

I do not have a nema number or a amps output rating on my generator however I do have 6.5750 on it, now what do I do for the conversion and how do I know what cord to use and what input to use? Can anyone help me, I'm thinking about running teck from the transfer switch outside to my plug but I'm...

How do I determine breaker amps on a 240v double breaker? [ 7 Answers ]

Hi, I have a new elec. Cooktop that needs 240V, 40 amps. Each pole of the double pole breaker for my cooktop circuit Says 30amps. So can this 240v circuit support 60 amps, or just 30? Thanks!

Breaker Box Amps rating & Number of breakers installed [ 1 Answers ]

I have a question in regards to amps allowed in a breaker box. My breaker box has a label stating that the box has a maximum load of 200 amps, but that it is convertible. I really don't know what the convertible part means. If I look at the breakers installed, these add way more than 200 amps. ...


View more questions Search