    Blower works with heat does not work with air conditoner
    I have a YORK HVAC unit, the blower works fine when I have the heat on, however, when I put the air conditioner on, the inside blower doesn't work. No air comes out of the vent? Is there a control some where which dictates the blower to go on and off based on heating or AC?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    May 24, 2010, 05:59 AM

    I would suspect and test at the thermostat.
    Blower is usually the green wire, when set to heat or cool, red connects to green.
    cpandya's Avatar
    cpandya Posts: 3, Reputation: 1
    New Member
     
    #3

    May 24, 2010, 01:03 PM
    There are four wires Red, Yellow, Green and White. There are 5 slots to hook up these wires, namely W for White, Y for Yellow, W for White and two reds( R and Ro), the red is connected to Ro and all others are connected accordingly, White in W, Yellow in Y and Green in G. Should I connect the red with green as well? And leave both R and Ro empty?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    May 24, 2010, 01:24 PM

    Likely Red is from transformer, green is blower fan, white is heat, and yellow for cooling. Is this a new thermostat, any new wiring, or problem just developed?
    cpandya's Avatar
    cpandya Posts: 3, Reputation: 1
    New Member
     
    #5

    May 24, 2010, 04:15 PM
    I moved in this house in January, as it was cold outside, inspector did not check the air conditioner saying the oil in the compressor is all jammed due to cold, so won't be able to check it. However, when I checked in the hot weather, the blower fails to kick in. May be wiring was altered/changed/worked on, not sure about it though. Also there a two zones where the problem is, not sure if it helps in diagnosis. Thanks for your responses.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #6

    May 25, 2010, 05:43 AM

    The fan relay is out on the control board.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    May 25, 2010, 05:47 AM

    For a test, you could disconnect wiring from thermostat, connect red, yellow and green. That should get blower and compressor going, if so, problem is in the thermostat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Blower works on heat butnot a/c [ 1 Answers ]

On my central unit the heat works fine but turn on the a/c the blower motor won't come on. I replaced the relay.

Blower will not work with a/c but works with heat [ 2 Answers ]

We have a coleman evcon blend air II furnace. The blower motor will not kick on when the a/c is turned on, but will kick on when switched over to heat. The outside unit is working. We have replaced the thermostat and a relay switch and still no fix. Any ideas?

Heat blower works ac blower won't shut off. [ 1 Answers ]

Hello, I am having trouble with my RTH230B Honeywell. I have a Gas furnace and an outdoor ac unit hooked up to a blower and the blower has a heat off cool setting on a switch on it. Our when set on heat everything works as it should. BUT as soon as I turn the blower to cool it turns on and...

Will increasing the air intake allow the air conditoner to cool the house better? [ 1 Answers ]

We have a 2400 sq ft house that was built in 2000. We were told by an air conditioner sales rep that our air conditioner is almost too small for our house. However, he said that if we increase the air intake by cutting another hole in the ceiling it should improve it. Meaning that on the hot 107...

Blower fan works in A/C but not heat [ 8 Answers ]

A couple of weeks ago my Lennox G20Q3E-75-1 was acting up. Gas valve was cycling when calling for heat and then once satisfied and the main burners went out the pilot light was staying lit. I thought it might be the flame sensor as far as the gas valve cycling and didn't want to tear into it so I...


View more questions Search