New Member
|
|
May 17, 2010, 07:07 PM
|
|
Gibson GQ3RA-24K Wire size?
I've got a Gibson GQ3RA-24K I've been using it with out the heat coils. It's on a double 30amp breaker with 10gage wire. I'm wanting to hook the heat coils up but don't know if that wire will be enough. What size wire should I have?
|
|
 |
Ultra Member
|
|
May 17, 2010, 07:13 PM
|
|
What size heat strip do you have? You can run a 5 kw on a 30 amp.
|
|
 |
New Member
|
|
May 17, 2010, 08:07 PM
|
|
I'm not really sure. So with 5k it will run the heat pump and coil on 30?
|
|
 |
New Member
|
|
May 17, 2010, 08:08 PM
|
|
It's not marked on the tag like it should be.
|
|
 |
New Member
|
|
May 17, 2010, 08:55 PM
|
|
Also when I do hook the coils up how do I check to see if they work, they don't kick in unless it's to cold for the heat pump right?
|
|
 |
Ultra Member
|
|
May 18, 2010, 05:33 AM
|
|
 Originally Posted by Jeremy126
Also when I do hook the coils up how do I check to see if they work, they don't kick in unless it's to cold for the heat pump right?
If there is more then 1 coil it is larger then a 5kw. Once it is installed turn the t-stat to emergency heat. This will bring the electric elems on if wired correctly.
|
|
 |
New Member
|
|
May 18, 2010, 08:00 AM
|
|
My thermostat is a ritetemp it works for heat pumps with aux heat but has no emergency heat.
|
|
 |
New Member
|
|
May 18, 2010, 08:02 AM
|
|
It's a 6022 ritetemp.
|
|
 |
Ultra Member
|
|
May 18, 2010, 12:56 PM
|
|
If it is set up fro aux heat all you should need to do is turn the heat setpoint about 5 degrees warmer then the temp inside and the aux should come on.
|
|
 |
New Member
|
|
May 18, 2010, 01:48 PM
|
|
Thanks.
I've got two coils so can I set it up to run just one. With just one the 30 amp break will be able to power the coil and the compressor?
|
|
 |
New Member
|
|
May 18, 2010, 04:56 PM
|
|
So I've got two coils does that mean it's 8 or 10kw?
What does the 60`C CU , 75`C CU ,and 90`C CU mean?
|
|
 |
Ultra Member
|
|
May 18, 2010, 05:32 PM
|
|
Yes I would say it is a 10. Where are you seeing the c cu?
|
|
 |
New Member
|
|
May 19, 2010, 09:22 AM
|
|
It's on page 5 of the link you posted. Across the top of the table.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Wire size & conduit size for 60 am subpanel 150 from source
[ 9 Answers ]
Indiana question:
I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement.
What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run.
John
Sub Panel AMP Size and Supply Wire Size
[ 1 Answers ]
I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...
Vintage stove- 3 wire 220v, what size wire?
[ 1 Answers ]
We recently purchased a vintage Crosley range. The old wire was a 3-wire 220v, connected to terminals in the back- the black and red wires were actually 6 or so copper strands, and the white was a silver metal. My question is, what amperage do you think I need? Will 10 be enough?
Thanks for your...
4 wire home service entrance wire size
[ 1 Answers ]
Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?
View more questions
Search
|