  • May 17, 2010, 07:07 PM
    Jeremy126
    Gibson GQ3RA-24K Wire size?
    I've got a Gibson GQ3RA-24K I've been using it with out the heat coils. It's on a double 30amp breaker with 10gage wire. I'm wanting to hook the heat coils up but don't know if that wire will be enough. What size wire should I have?
  • May 17, 2010, 07:13 PM
    Joshdta

    What size heat strip do you have? You can run a 5 kw on a 30 amp.
  • May 17, 2010, 08:07 PM
    Jeremy126

    I'm not really sure. So with 5k it will run the heat pump and coil on 30?
  • May 17, 2010, 08:08 PM
    Jeremy126

    It's not marked on the tag like it should be.
  • May 17, 2010, 08:55 PM
    Jeremy126

    Also when I do hook the coils up how do I check to see if they work, they don't kick in unless it's to cold for the heat pump right?
  • May 18, 2010, 05:33 AM
    Joshdta
    Quote:

    Originally Posted by Jeremy126 View Post
    Also when I do hook the coils up how do I check to see if they work, they don't kick in unless it's to cold for the heat pump right?

    If there is more then 1 coil it is larger then a 5kw. Once it is installed turn the t-stat to emergency heat. This will bring the electric elems on if wired correctly.
  • May 18, 2010, 08:00 AM
    Jeremy126

    My thermostat is a ritetemp it works for heat pumps with aux heat but has no emergency heat.
  • May 18, 2010, 08:02 AM
    Jeremy126

    It's a 6022 ritetemp.
  • May 18, 2010, 12:56 PM
    Joshdta

    If it is set up fro aux heat all you should need to do is turn the heat setpoint about 5 degrees warmer then the temp inside and the aux should come on.
  • May 18, 2010, 01:48 PM
    Jeremy126

    Thanks.

    I've got two coils so can I set it up to run just one. With just one the 30 amp break will be able to power the coil and the compressor?
  • May 18, 2010, 03:06 PM
    Joshdta

    Acorrding to this for a 5 kw you will need a 40 amp breaker. Take a look.

    http://www.nordyne.com/literature/a777a.pdf
  • May 18, 2010, 04:56 PM
    Jeremy126

    So I've got two coils does that mean it's 8 or 10kw?

    What does the 60`C CU , 75`C CU ,and 90`C CU mean?
  • May 18, 2010, 05:32 PM
    Joshdta

    Yes I would say it is a 10. Where are you seeing the c cu?
  • May 19, 2010, 09:22 AM
    Jeremy126

    It's on page 5 of the link you posted. Across the top of the table.