    Gibson GQ3RA-24K Wire size?
    I've got a Gibson GQ3RA-24K I've been using it with out the heat coils. It's on a double 30amp breaker with 10gage wire. I'm wanting to hook the heat coils up but don't know if that wire will be enough. What size wire should I have?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    May 17, 2010, 07:13 PM

    What size heat strip do you have? You can run a 5 kw on a 30 amp.
    Jeremy126's Avatar
    Jeremy126 Posts: 13, Reputation: 1
    New Member
     
    #3

    May 17, 2010, 08:07 PM

    I'm not really sure. So with 5k it will run the heat pump and coil on 30?
    Jeremy126's Avatar
    Jeremy126 Posts: 13, Reputation: 1
    New Member
     
    #4

    May 17, 2010, 08:08 PM

    It's not marked on the tag like it should be.
    Jeremy126's Avatar
    Jeremy126 Posts: 13, Reputation: 1
    New Member
     
    #5

    May 17, 2010, 08:55 PM

    Also when I do hook the coils up how do I check to see if they work, they don't kick in unless it's to cold for the heat pump right?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #6

    May 18, 2010, 05:33 AM
    Quote Originally Posted by Jeremy126 View Post
    Also when I do hook the coils up how do I check to see if they work, they don't kick in unless it's to cold for the heat pump right?
    If there is more then 1 coil it is larger then a 5kw. Once it is installed turn the t-stat to emergency heat. This will bring the electric elems on if wired correctly.
    Jeremy126's Avatar
    Jeremy126 Posts: 13, Reputation: 1
    New Member
     
    #7

    May 18, 2010, 08:00 AM

    My thermostat is a ritetemp it works for heat pumps with aux heat but has no emergency heat.
    Jeremy126's Avatar
    Jeremy126 Posts: 13, Reputation: 1
    New Member
     
    #8

    May 18, 2010, 08:02 AM

    It's a 6022 ritetemp.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #9

    May 18, 2010, 12:56 PM

    If it is set up fro aux heat all you should need to do is turn the heat setpoint about 5 degrees warmer then the temp inside and the aux should come on.
    Jeremy126's Avatar
    Jeremy126 Posts: 13, Reputation: 1
    New Member
     
    #10

    May 18, 2010, 01:48 PM

    Thanks.

    I've got two coils so can I set it up to run just one. With just one the 30 amp break will be able to power the coil and the compressor?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #11

    May 18, 2010, 03:06 PM

    Acorrding to this for a 5 kw you will need a 40 amp breaker. Take a look.

    http://www.nordyne.com/literature/a777a.pdf
    Jeremy126's Avatar
    Jeremy126 Posts: 13, Reputation: 1
    New Member
     
    #12

    May 18, 2010, 04:56 PM

    So I've got two coils does that mean it's 8 or 10kw?

    What does the 60`C CU , 75`C CU ,and 90`C CU mean?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #13

    May 18, 2010, 05:32 PM

    Yes I would say it is a 10. Where are you seeing the c cu?
    Jeremy126's Avatar
    Jeremy126 Posts: 13, Reputation: 1
    New Member
     
    #14

    May 19, 2010, 09:22 AM

    It's on page 5 of the link you posted. Across the top of the table.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...

Vintage stove- 3 wire 220v, what size wire? [ 1 Answers ]

We recently purchased a vintage Crosley range. The old wire was a 3-wire 220v, connected to terminals in the back- the black and red wires were actually 6 or so copper strands, and the white was a silver metal. My question is, what amperage do you think I need? Will 10 be enough? Thanks for your...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search