    How far can I run 240v 30 amps in a 10 gauge or 8 gauge line?
    I'm supplying electric to a remote building with no other power source. The generator supplies 240v 30 amp. How far away can I keep the generator outside with a 10 gauge line connecting to a service panel? What if I use 8 gauge? The building is used infrequently and I run an air compressor a few lights and occasional shop tool.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    May 10, 2010, 12:37 PM
    How far away? Is that a trick question? I'd keep less than 60 feet for the 10 gauge... and that's for occasional use. If you go the 8 gauge, 100 feet would be about the max... same load situation. The draw of the air compressor motor while starting would be the biggest issue. The closer you can put the generator to the building is the best way to go, in cost and efficiency. Is this a hard wired project or are you using a cord? 4 wire cords get a bit pricy.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    May 10, 2010, 02:46 PM

    For 30 amps

    #10 wire = 40'
    #8 wire = 64'
    #6 wire =101.7
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    May 10, 2010, 04:47 PM
    3% drop is the most you should have in your run. Here's a calculator I have used to help with the calculation. 404page.html
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #5

    Jan 31, 2011, 07:53 AM
    Personally, I would run 4ga copper. It's expensive but is rated at 100 amps and would not offer much voltage drop. If you don't want to use copper because of the expense, run 2/0 aluminum.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

12 gauge wire @ 160 ft with 120 v and 14 amps will it work [ 1 Answers ]

Need to know if the amperage will be enough when it gets to the pump off a 20 amp breaker

Can I attach a 14 gauge light into a 12 gauge circuit [ 3 Answers ]

Is it acceptable to attach a 14 gauge light in a 12 gauge 20 amp circuit? I am finishing my basement and using 12 gauge wire throughout. When I bought my light fixtures, they are wire with 14 gauge wire. Is it safe to use these or do I need to get different light fixtures?

Connecting 12 gauge and 14 gauge wire [ 4 Answers ]

Is it ever acceptable to attach 14 gauge to 12 gauge wire? I have a remodel situation where I have a 20 amp/12 gauge wired circuit powering outlets only. I want to tap off the end-of-run outlet to power an electric-venting skylight. The skylight comes with 14/2 wire. Can I tap off the 20 amp...

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...


View more questions Search