    Distance between circuit breaker box and water meter?
    We are redoing an old small house in which the fuse box is under a kitchen cabinet along with the water meter. We are replacing the fuse box to a 100A circuit breaker box. Right now the fuse box and the water meter are located 12 inches apart. How far away from the water meter is the breaker box required to be per the NEC? We were going to put it back in the same place but a friend thought the NEC had other requirements. Our current location is Toledo, OH.
    Bec2163's Avatar
    Bec2163 Posts: 4, Reputation: 1
    New Member
     
    #2

    May 8, 2010, 11:57 AM
    Distance between circuit breaker box and water meter
    We are redoing an old small house in which the fuse box is under a kitchen cabinet along with the water meter. We are replacing the fuse box to a 100A circuit breaker box. Right now the fuse box and the water meter are located 12 inches apart. How far away from the water meter is the breaker box required to be per the NEC? We were going to put it back in the same place but a friend thought the NEC had other requirements. Our current location is Toledo, OH.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    May 8, 2010, 12:21 PM

    The panel can be right next to the water meter, but you must still meet clearances.
    There must be a clear space at the panel 30" wide and 36" deep, and 6'6" high.
    The panel need not be centered in the 30" wide space.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    May 8, 2010, 04:48 PM

    A 30" wide by 36" deep working space is required in front of the electric panel. The panel can be as far away from the water meter as desired. The two are not related.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    May 8, 2010, 05:57 PM

    Translation, the panel cannot be inside a kitchen cabinet.

    Where does the electric service enter the residence, you want the meter as close to that point as possible.
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #6

    May 8, 2010, 06:10 PM

    Threads merged, please only start one thread for the same question
    Bec2163's Avatar
    Bec2163 Posts: 4, Reputation: 1
    New Member
     
    #7

    May 8, 2010, 06:52 PM
    Quote Originally Posted by donf View Post
    Translation, the panel cannot be inside a kitchen cabinet.

    Where does the electric service enter the residence, you want the meter as close to that point as possible.
    *****
    The service currently comes into the house on an exterior wall right behind the cabinet. The water meter is in this cabinet as well.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    May 9, 2010, 12:29 PM

    Bec,

    In order to be in compliance with the NEC you will have to relocate the panel from under the sink counter.

    You need to mount the panel where there is a minimum of 6' from floor to ceiling. If you have a suspended ceiling, below the 6' level, that is acceptable.

    There has to be a 3' side to side clearance in front of the panel (the panel can be off-center within that 3' zone.

    There needs to be at least a 3' deep space from in front of the panel extending toward the middle of the room.

    Contact your Power Company to have them tell you where they are willing to move the service to.

    Then contact the LHJ, file a project plan with them and then get a permit.

    Since you are moving the panel, all of the associated with the panel will have to relocated also.
    Bec2163's Avatar
    Bec2163 Posts: 4, Reputation: 1
    New Member
     
    #9

    May 9, 2010, 05:42 PM
    Quote Originally Posted by donf View Post
    Bec,

    In order to be in compliance with the NEC you will have to relocate the panel from under the sink counter.

    You need to mount the panel where there is a minimum of 6' from floor to ceiling. If you have a suspended ceiling, below the 6' level, that is acceptable.

    There has to be a 3' side to side clearance in front of the panel (the panel can be off-center within that 3' zone.

    There needs to be at least a 3' deep space from in front of the panel extending toward the middle of the room.

    Contact your Power Company to have them tell you where they are willing to move the service to.

    Then contact the LHJ, file a project plan with them and then get a permit.

    Since you are moving the panel, all of the associated with the panel will have to relocated also.
    *********************

    Don, thanks for the information. The next question we have is can the breaker box be located on an outside wall or does it have to be an internal wall?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #10

    May 9, 2010, 06:31 PM

    Yes, a main panel can be located outside. Check with your local power company about where they are willing to put the service line to your home, that will lock your decision as to where the service panel can be installed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cable to use from meter base to breaker box [ 16 Answers ]

I am moving my current breaker box to the outside of my house. It will sit approimatly 1 foot from my meter base, I will need about 10 feet of cable to make the run (I think). I just need to know what kind of cable I need to use. And if I need to have it in a conduit. I have look in the NEC,...

Outdoor electrical circuit 400' from main meter box [ 3 Answers ]

I want to add two circiuts to a junction box , apx 400' from a pass through electrical box on my property, I had put in underground 1 1/4 cunduit with a pull box every 100 feet when the house was built. What size cable should be used for this, it will need to handle 2- 20 amp circuits

Upgrading from a fuse box to a circuit breaker box [ 1 Answers ]

How do I upgrade my fuse box in my home


View more questions Search