    I am running a 60 amp double pole feeder to my outbuilding.
    I am running a 60 amp double pole breaker to my outbuilding 190' away. I figure I should use #4 copper use wire for the ungrounded conductors. The legs in my subpanel figure to 42 amps on one leg and 29 on the other if my calculations are correct. These are figured on 180 va for duplex outlets (20 of them) and 125% va of my max incandescent lighting(3150 max va). I have no appliances or fastened in place load in the outbuilding. Should I use #4 copper use fro the grounded conductor? Is #8 copper use adaquate for the equipment grounding conductor?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Apr 30, 2010, 07:06 PM
    190' is a long run... but #4 will be OK for the 240 service... and #8 is OK for the egc. Remember that you need to separate the ground and the neutral at the outbuilding panel, and you also need a grounding rod at that location. How many circuits do you intend on having in the outbuilding? If you have no appliances or hardwired equipment in this building, why is the amperage so high? Certainly it's not lighting, is it?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    May 1, 2010, 04:38 AM
    Based on 20 outlets at 180 VA each, and 3150 VA of lighting, totals 56.25 amps of 120 volt load. Then you listed 71 amps of calculated load. So not sure how you arrived at 42 and 29 amps per leg.

    Run #4 for both ungrounded and the grounded conductors.
    karmelcopia's Avatar
    karmelcopia Posts: 14, Reputation: 1
    New Member
     
    #4

    May 1, 2010, 05:03 AM

    I calculated the incandescent lighting load as continuous.(3150 * 1.25). Although thus would be a maximum if all lights were on with the maximum wattage lamps installed.
    karmelcopia's Avatar
    karmelcopia Posts: 14, Reputation: 1
    New Member
     
    #5

    May 1, 2010, 05:08 AM

    I am using this building with some band and recording equipment.I tried to keep the outlets in some areas on separate circuits but the same leg to reduce noise and interference that is why the legs are a little unbalanced. That is also why I prefer incandescent over noisy ballasts.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #6

    May 1, 2010, 08:15 AM
    When you say "noisy" are you referrring to the transformer hum, or electrical noise? Neither will be a problem with electronic ballasts, and you can cut your lighting load easily by 40%. Incandescents also produce more heat per watt, if cooling the building is an issue.
    karmelcopia's Avatar
    karmelcopia Posts: 14, Reputation: 1
    New Member
     
    #7

    May 1, 2010, 05:07 PM

    Trying to eliminate any electrical noise in the equipment from any external sources. Ei. Keep equipement on same leg, eliminate the transformers. Also hoping keeping equipment on the same leg will eliminate nasty microphone shocks. They really sting your lips.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #8

    May 1, 2010, 06:49 PM
    Proper grounding will take care of the noise issue and proper polarity should take care of the mic shocks. I played drums in a band years ago.. and during a wedding gig our lead singer got a mic. Shock... and dropped the F-bomb... while the newleyweds were dancing... apparently only the band found it funny.
    karmelcopia's Avatar
    karmelcopia Posts: 14, Reputation: 1
    New Member
     
    #9

    May 3, 2010, 04:33 AM

    I guess he bombed a bomb on them... baby. Hehe
    karmelcopia's Avatar
    karmelcopia Posts: 14, Reputation: 1
    New Member
     
    #10

    May 3, 2010, 04:33 AM

    Dropped a bomb on them ooops

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker [ 10 Answers ]

:confused: I keep getting the GFCI breaker tripping after wiring my hot tub. I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When I wire...

30 Amp Double Pole Breaker is hot and tripping [ 10 Answers ]

Hi, I just got a Maytag Neptune Dryer a week ago. I have it plugged in to our old dryer outlet (which was replaced less than a year ago) which is 3 prong. The dryer voltage is 240 volts and I am running it on a 30 amp double pole breaker. The problem is, this is new electrical wiring and a...

20 amp double pole gfci [ 9 Answers ]

I am working on an addition and am installing a whirlpool tub. The tub requires 2 - 20 amp GFCI protect circuits: 1 for the pump and 1 for the heater. I ran 12/3 wire in the walls thinking I could have the BLACK wire go from 1 GFCI breaker to the pump outlet and the RED wire go from a 2nd GFCI...

Double pole 15 amp GFCI [ 1 Answers ]

I read the other note on gfci, but I have a different problem. I am installing a compressor outside the house in a shed, and I want to install an outside electrical socket on my outside wall of the house. The compressor requres 240V 15 Amps. I was planning on running a large extension cord to the...

240 20 Amp double pole hookup [ 3 Answers ]

So this site is great, thanks Ok my next question is if I have a 12-2 wire at the baseboard then I would hook-up the dual-pole 20Amp at the box with both the white and black into each of the breakers connection and of course the ground to ground, no nuetral, right? Steve


View more questions Search