I am running a 60 amp double pole feeder to my outbuilding.
I am running a 60 amp double pole breaker to my outbuilding 190' away. I figure I should use #4 copper use wire for the ungrounded conductors. The legs in my subpanel figure to 42 amps on one leg and 29 on the other if my calculations are correct. These are figured on 180 va for duplex outlets (20 of them) and 125% va of my max incandescent lighting(3150 max va). I have no appliances or fastened in place load in the outbuilding. Should I use #4 copper use fro the grounded conductor? Is #8 copper use adaquate for the equipment grounding conductor?