New Member
|
|
Apr 3, 2010, 12:11 PM
|
|
Not getting proper voltage to dryer after rewire.
I just wired a new breaker box from the service box and have connected my dryer to it. Now my dryer won't heat. I tested the 220 outlet with a multimeter and between either hot lead and neutral I get a reading of 120v but between both hot leads I get nothing. I'm told that it should read 240. What could be the problem?
|
|
 |
Home Improvement & Construction Expert
|
|
Apr 3, 2010, 12:25 PM
|
|
What kind of cable are you using?
Are you using a double breaker?
|
|
 |
New Member
|
|
Apr 3, 2010, 12:28 PM
|
|
8 or 10 gauge cable and double 40 amp breakers
|
|
 |
Printers & Electronics Expert
|
|
Apr 3, 2010, 12:46 PM
|
|
Well for one very simple thng, if you have an analog meter, your meter may not be set correctly.
However if it is a digital meter, then most likely you do not have to set it.
What is the voltage it is set for
|
|
 |
Home Improvement & Construction Expert
|
|
Apr 3, 2010, 12:49 PM
|
|
If you are using a double breaker with the hot leads connected to the breaker and the white connected to the neutral you must have incorrectly wired the receptacle. I assume you are checking for voltage through the receptacle. Remove from box and check voltage at the terminals.
You said double 40 amp breakers. Do you mean a double 40 amp breaker.
Wire should be 8/3 (that's 3 conductors and a ground, 4 wires)
|
|
 |
Electrical & Lighting Expert
|
|
Apr 3, 2010, 12:53 PM
|
|
I bet this is GE or FPE panel and the breaker is installed wrong. The breaker MUST contact both panel busses. Both these style breakers are capable of being installed incorrectly and only contacting one buss.
Also, change the 40A breaker to a 30A.
|
|
 |
New Member
|
|
Apr 3, 2010, 01:37 PM
|
|
It is a GE panel. I'm going to try to upload a photo to see if that will help. How can I tell if the breaker is installed incorrectly? Dryer circuits are on top.
Photo: Breaker Box Dryer is Top 2 circuits
|
|
 |
Home Improvement & Construction Expert
|
|
Apr 3, 2010, 02:19 PM
|
|
That's not a double breaker. A double breaker is two breakers made into one with a handles tied together.
If you look at the way those two breakers contact the circuit panel, they contact the same leg of the incoming power. Giving you 120 volts.
The way the panel is made, one breaker space contacts one leg and the next space down contacts the other leg. Giving you 240 volts.
Get a 30 amp double breaker. Remove the two 40 breakers. Move all the breakers on the left hand side down one space. Plug in the 30 double in the top two spaces.
|
|
 |
Electrical & Lighting Expert
|
|
Apr 3, 2010, 03:02 PM
|
|
Also, your panel is wired wrong.
1) The neutrals and ground MUST be on separate bars in this sub-panel.
2) The existing bar must be used as the neutral bar and remain un-bonded. IOW leave out the green screw that came with the box.
3) Get a new dedicated ground bar and screw it directly to the panel box.
That panel is nice and neat, but the mistakes and violations concern me.
|
|
 |
Ultra Member
|
|
Apr 3, 2010, 03:48 PM
|
|
Seems like a pretty aggressive project for a HO who really isn't sure of how a panels buss bars are arranged, and of course the obvious grounding issue. Nevertheless the panel installation was neat and clearly labeled.
|
|
 |
New Member
|
|
Apr 3, 2010, 08:23 PM
|
|
hkstroud, thank you! You saved the day. Dryer works perfectly now. These newer panels are much different than the ones I'm used to.
|
|
 |
Uber Member
|
|
Apr 4, 2010, 04:23 AM
|
|
So, now that the dryer works, will you be separating the grounding as suggested?
Neatness means nothing when done wrong.
A photo of the proper circuit breaker would be great help in illustrating to other.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Proper Grouding of 30a dryer circuit
[ 3 Answers ]
Hi all,
I'm installing a 30a 2-pole breaker in my breaker panel to be a dedicated line for a clothes dryer. The panel is Square D type QO with 100a main breaker and 20 breaker slots.
Clothes dryer manual says to use 10-3 cable, make sure to connect that 4th wire to the ground bar, or use...
Dryer Voltage
[ 1 Answers ]
I just purchased a used Kenmore dryer built in 2003. It has markings for 120 and 240 volts. Is this unit dual voltage, and will my existing 220 volt plug wire in with no problems as long as I match the red and black wires? I believe the white wire goes to the center post and the ground will...
Kenmore Dryer voltage
[ 4 Answers ]
Good morning!
Excuse me, I don't speak English and I am writing of Brazil with the help of a translating program.
A friend gave me a drying one, Kenmore Dryer 80 Series, MOD 110.62852100, to SER. ML3716205, TYPE DWSR-HE-2406028-CV54, and my doubt is on the voltage of this machine, I...
Best rewire solution to avoid voltage drop
[ 9 Answers ]
I need to replace existing wiring in a bedroom/office. The panel is located in a basement and NM can be run up a chase to the attic. From the attic, access to receptacle locations can be made through the wall plates down to the receptacle locations. The question concerns cable length and the best...
View more questions
Search
|