    Limitation of location of Service Panel near Chimney?
    Is there any limitation with respect to locating a service panel or NM wire near a masonry chimney? I'm installing a new service panel in my house and the ideal location would be set in the wood framing I have around my center chimney.

    The Chimney is boxed in with wood framing and the wiring to the service panel would run up and down this channel to the second floor and crawlspace.

    The chimney is no longer used - it was originally used for a oil furnace in the crawlspace but the furnace has since been replaced with an outside venting gas boiler on the first floor. Unfortunately, I don't think the Inspector will take this fact into consideration...

    Appropriate fire stops would be used between floors...

    Tom
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 30, 2010, 09:23 AM
    I don't see a problem with what you propose.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Mar 30, 2010, 11:57 AM

    Question,

    Don't the POCO and NEC have guidelines regarding the position of the Service Panel with respect to the Service Entry Point?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Mar 30, 2010, 02:15 PM
    No, the NEC requires the Service Disconnecting Means, AKA Main Breaker, to be installed immediately as the service entrance conductors enter the building, or be outdoors.

    Utility companies will always refer to the NEC.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Mar 30, 2010, 06:16 PM

    Thanks, that also explains a little more for me about that problem in Canada where the poster used a 200 Amp switch to feed three different panelboards.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service panel location and or re-location codes [ 8 Answers ]

I just built a new addition on my home, bigger than my existing home. I want to move the service panel from the old basement to the new basement, I would like to do this using the 4/0-4/0-4/0 aluminum service wire run in conduit, it is about 45 to 55 feet. What is the code on this? Also what is the...

Adding another panel from a 200 amp service panel [ 3 Answers ]

Hi everyone, this is my first post. I have a 60 x 100 ft shop that has a 200 amp service fed in from the pole. Well I added a living space in the shop, which is about 720 sq ft. I plan on doing all the wiring myself and need a little advice on what kind of panel I should use? The living quarters...

Need to change panel box location in service upgrade because old one has only inches to I [ 7 Answers ]

4 electricians gave estimates to upgrade a service box from 100 to 200 amps. Only one felt that the new panel should definitely be moved because the old one is smaller and sits up against the gas meter piping on one side and the corner of the garage on the other, leaving only inches around the...

200 AMP Service panel to 200Amp Sub Panel [ 1 Answers ]

I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling. 2 Questions 1. Is there any ristriction on running a 200AMP inside house to garage ? 2. I got a dirt cheap subpanel that has...

Location of upgraded service panel [ 2 Answers ]

I am upgrading the electrical service from 100 to 200 amps and am in question of my new desired panel location. I would like to place it on an exterior wall behind the new meter location. The power company has said my new meter location is fine. I was wondering if it is code to have the panel...


View more questions Search