  • Mar 30, 2010, 07:51 AM
    TomWS
    Limitation of location of Service Panel near Chimney?
    Is there any limitation with respect to locating a service panel or NM wire near a masonry chimney? I'm installing a new service panel in my house and the ideal location would be set in the wood framing I have around my center chimney.

    The Chimney is boxed in with wood framing and the wiring to the service panel would run up and down this channel to the second floor and crawlspace.

    The chimney is no longer used - it was originally used for a oil furnace in the crawlspace but the furnace has since been replaced with an outside venting gas boiler on the first floor. Unfortunately, I don't think the Inspector will take this fact into consideration...

    Appropriate fire stops would be used between floors...

    Tom
  • Mar 30, 2010, 09:23 AM
    tkrussell
    I don't see a problem with what you propose.
  • Mar 30, 2010, 11:57 AM
    donf

    Question,

    Don't the POCO and NEC have guidelines regarding the position of the Service Panel with respect to the Service Entry Point?
  • Mar 30, 2010, 02:15 PM
    tkrussell
    No, the NEC requires the Service Disconnecting Means, AKA Main Breaker, to be installed immediately as the service entrance conductors enter the building, or be outdoors.

    Utility companies will always refer to the NEC.
  • Mar 30, 2010, 06:16 PM
    donf

    Thanks, that also explains a little more for me about that problem in Canada where the poster used a 200 Amp switch to feed three different panelboards.