New Member
|
|
Feb 13, 2010, 09:18 AM
|
|
My ac/heat keeps running
I live in Florida a/c & heat are same unit. The unit was serviced one month, go problems, cleaned and working fine. However, on heat mode, it frosts up and the fan never runs. My neighbors fan runs, even on heat. I was told during service this is normal. I suspect I have become more aware of the variations now. Is this normal?? Thanks
|
|
 |
Ultra Member
|
|
Feb 13, 2010, 09:40 AM
|
|
Brand/model#? Are you referring to the outdoor fan? If this is a heat pump system, it should be running at least part-time. If the unit is equipped with a vapor pressure switch, it may cycle the outdoor fan to control heat absorption in milder temperatures.
|
|
 |
New Member
|
|
Feb 13, 2010, 09:52 AM
|
|
 Originally Posted by KC13
Brand/model#? Are you referring to the outdoor fan? If this is a heat pump system, it should be running at least part-time. If the unit is equipped with a vapor pressure switch, it may cycle the outdoor fan to control heat absorption in milder temperatures.
It is a Carrier/Radco FA4ANF036. Yes outdoor fan, I have not seen it run at all. Temps outside have been 30s & 40s. In these temps should the fan be turning, or is it normal to not be, in these temps and on Heat mode
|
|
 |
Ultra Member
|
|
Feb 13, 2010, 10:12 AM
|
|
The number you provided is for the indoor unit. This info, along with the frost you see on the outdoor unit, suggests you have a heat pump system. The outdoor fan should be running anytime the system is operating in a heating or cooling cycle. Try this: set thermostat mode selector to COOL & lower set temperature to cause system to run. Does outdoor fan run? Listen for any operating sounds, such as compressor running.
|
|
 |
New Member
|
|
Feb 14, 2010, 04:10 AM
|
|
 Originally Posted by KC13
The number you provided is for the indoor unit. This info, along with the frost you see on the outdoor unit, suggests you have a heat pump system. The outdoor fan should be running anytime the system is operating in a heating or cooling cycle. Try this: set thermostat mode selector to COOL & lower set temperature to cause system to run. Does outdoor fan run? Listen for any operating sounds, such as compressor running.
Thanks
|
|
 |
Ultra Member
|
|
Feb 14, 2010, 08:58 AM
|
|
 Originally Posted by ckt1940
Thanks
You're welcome... umm... what happened? Did the fan run? :confused:
|
|
 |
New Member
|
|
Feb 14, 2010, 12:26 PM
|
|
 Originally Posted by KC13
You're welcome...umm...what happened? Did the fan run? :confused:
Yes it runs now, our temps have been abnormally cold at night, high 20s to mid 40s. From what I read this can be a problem with heat pumps operating properly.
Thanks again,
Frank
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Heat won't shut off on heat pump and outside fan not running
[ 2 Answers ]
My heat pump runs continually inside in heat mode but the fan motor outside won't run. If I make it cooler in the house (65 or so) it will run properly. If the a/c is on and I lower it to 70 inside the outside motor won't work again but the compressor unit runs. Have already replaced fan motor...
Heat pump not running
[ 1 Answers ]
I turn the heat on set 5 degree above the room temp. the thermalst. Try to kick but neither outside unit nor the blower running. I turn on the fan only the blower run, I replace the new contactor it not run, I try to push & hold the click the system run. Give me some idea, thank you!
Heat pump running
[ 1 Answers ]
I have a heat pump system everything works great. However, why does the fan come on when the system is off? It will run about every 20 minutes and it acts like its going through a cycle. Is this normal? I thought maybe a contact switch but I don't think that it has one. Any suggestions or tell me...
View more questions
Search
|