    how does the thermostat close the contacts on the contactor
    how does it start the unit since the contactor is not energized?
    how is the complete circuit getting closed/

    I know where the wires from the thermostat connect to that panel with the R, Y, W, G, C erminals but I donot undserstand how the whole thing works together

    maybe someone could explain it in detail please

    TIA p
    TIA = thanks in advance
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jan 30, 2010, 04:03 PM

    This applies to many, not all, numbers, colors and letters may be different.
    Basically you usually have a 240 volt to 24 volt transformer used to control the contactors, one side of the transformer may get power continuously to one side of the contactors, the other side of the transformer goes to the thermostat, usually a red, then when set to cool, it will place power to the green(to activate the Blower) and alco connect the blue or yellow for the compressor contactor.
    When set to heat, red at the thermostat connects to the g(green) for fan and to W(White for heat.
    When thermostat is set to cool, 24 volts should be at Compressor contactor coil to energize contactor, turning on compressor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Magnetic contactor [ 1 Answers ]

Is the computation of the load of magnetic contactors are the same with circuit breaker load calculation?

Contactor Replacement [ 6 Answers ]

I have received my new contatctor and am ready to replace it. There are two sides I see on it. L1 and L2, and T1 and T2. Any advice from the professionals before I swap it out. I am very happy with the results on my new fan, motor, and cap. Only the contactor remains. If the old contactor doesn't...

Why I do not have 24 volts to my contactor when my thermostat is on ihave a carrier h [ 2 Answers ]

Help from south cakalaka I have a carrier heat pumpand I am not getting 24 volts to my contactor and my thermostat is working

Illusions contacts VS Natural touch contacts [ 1 Answers ]

Hi! Any one got any info on Illusions opeque colored contacts and Natrual Touch opeque colored contacts? Because I want to order some but my budget is very slim. The discroption of the contacts says that they provide depth to the eye... which gives off the illusion that they color you have is the...

Gas line & dryer vent pipe - how close is too close? [ 1 Answers ]

I'm rerouting the gas dryer vent piping so that it will inside the adjoining stud wall. At the top of the wall the vertical exhaust pipe will be within an inch or two of the horizontal running copper gas supply line. Question - is there a minimum distance that the metal dryer exhaust pipe must...


View more questions Search