    EMT sizing
    Question concerning the use of 1” or 1 ¼” EMT. I’ve referenced the NEC tables for conduit fill, but I’m concerned about the ease of the wire pull, and the amp/derating factor, which I am not that familiar with, or if it even applies. Local code requires conduit. This is the set up:
    1. Apprx. 11 foot run between service disconnect and panelboard.
    2. Two 90 degree bends
    3. 100 amp service
    4. Feeders #4 copper labeled THHN
    5. Bonding #8 insulated labeled THHN

    So, for the above application- 1” or 1 ¼” emt? Thanks.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 6, 2010, 07:26 PM

    I would go with 1¼". 1" is legal but pushing it with two 90's.
    You'll likely be able to pull it in by yourself with 1¼". With 1" you'll definitely need help.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jan 6, 2010, 08:11 PM

    If that conduit is outside which I assume it is make sure the wire is THWN. Many times the wire is dual marked THHN/THWN.
    afscme's Avatar
    afscme Posts: 23, Reputation: 4
    New Member
     
    #4

    Jan 6, 2010, 08:30 PM

    I like things easy so the 1 1/4" it is. Yes, the wire is dual marked THWN-2 or THHN
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Jan 7, 2010, 08:08 AM

    Why are you using #4 cable? If you selected this cable size because of T 310.15 in the NEC you need to be aware that this is for service entrance only.

    If you are using this amperage to feed a sub-panel then you select the required cables size based on T 310.16.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Jan 7, 2010, 02:48 PM

    Don, many areas still allow the use of 310.15(B)(6) for feeders as well as service entrance, and rightfully so IMO.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Wires in emt [ 2 Answers ]

How many #12 wires in 1/2and3/4 metal tubing emt.allowed.

EMT pipe behind a shower [ 2 Answers ]

I have a concrete block house. I need an outside outlet on the other side of the wall from where the bathtub/shower will be. Is it OK to drop EMT pipe down from the attic and behind where the cement board will be in the shower? Thank you.

Rigid or EMT [ 2 Answers ]

Planning some remodeling. Main breaker panel, currently within five feet of the meter, may be moved approximately 12 feet due to the size of the panel and framing considerations. A listed service disconnect will be placed at the old panel location, and rigid used from meter to disconnect. ...

Plenum EMT Bushings? [ 3 Answers ]

I'm installing a wireless access point in a commercial environment on a drop ceiling. The space above the drop ceiling is plenum. The data jack for the access point is installed in an electrical box through a ceiling tile supported by a rod snapped onto the ceiling grid. I want to have the data...


View more questions Search