New Member
|
|
Dec 20, 2009, 01:25 PM
|
|
Nordyne Series CLG Furnace
Furnace runs (forces heat) and does not shut off. This is a heat-only system. Replaced Honeywell thermostat with an Ace Hardware Heat Only thermostat. Have adjusted heat anticipator to the setting listed on the furnace (.04). Still runs and does not shut off.
Thanks for any help.
|
|
 |
Heating & Air Conditioning Expert
|
|
Dec 20, 2009, 02:36 PM
|
|
If the furnace runs all the time and will not shut off by turning down the thermostat then the thermostat wiring might be shorted. Disconnect the RH or R and the W terminal wires from the furnace at the terminal strip. If you remove the wires and the furnace shuts off then the thermostat wiring is the problem and usually that means the wiring has shorted out.
|
|
 |
New Member
|
|
Jan 2, 2010, 06:58 AM
|
|
Thank you for your reply. Would you consider talking to my boyfriend by phone while he looks at the furnace? Thanks for considering. My email:
No posting of email addresses please.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 2, 2010, 08:29 AM
|
|
Did you disconnect the wire (s) and do the test mentioned in my other post?
|
|
 |
New Member
|
|
Jan 2, 2010, 08:53 AM
|
|
Yes.
Think I should mention that prior to it running constantly that it would do what I have seen mentioned on this website as a "short cycle". It would run, cut off for a short period (several seconds or a minute or so) and then turn on again.
|
|
 |
New Member
|
|
Jan 2, 2010, 08:55 AM
|
|
After my boyfriend disconnected the thermostat wires, it still runs constantly.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 2, 2010, 10:59 AM
|
|
Post the complete exact model number. I will see if I can look it up to see what parts it contains and which part might be causing the problem.
|
|
 |
New Member
|
|
Jan 2, 2010, 02:00 PM
|
|
Thank you.
Model FEHA-015HA-01
s/n FE9110-82272
|
|
 |
New Member
|
|
Jan 2, 2010, 02:00 PM
|
|
There is a CLG after Nordyne, think that is the series.
|
|
 |
Plumbing Expert
|
|
Jan 2, 2010, 02:52 PM
|
|
Is it just the blower that is running constantly, or are the burners also burning constantly? Is the house getting really hot, getting really cold, or just staying nice and comfy?
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 2, 2010, 03:49 PM
|
|
If that unit is a electric furnace then the heat sequencer section that controls the blower is stuck closed. It will probably look like this. If this is what is in the unit take the plastic end of a screwdriver and tap it gently a time or two and see if the blower goes off. Naturally turn the power off first.
|
|
 |
New Member
|
|
Jan 2, 2010, 04:30 PM
|
|
This is a heat-only furnace. Not central air, not heat pump. I don't know if the model and s/n indicate the age of the furnace, but I do know that the trailer is late 70's-early 80's.
|
|
 |
New Member
|
|
Jan 2, 2010, 04:42 PM
|
|
mygirlsdad77: blower runs constantly, heats up to around 70 or so (where thermostat is set), but does not quit blowing.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 2, 2010, 06:35 PM
|
|
As mentioned before the sequencer OR contactor that controls the unit might be stuck shut. This happens when the contacts weld themselves together and on an older unit this happens quite a bit since the contacts have been well used.
I have no wiring diagram for that old of a unit but I know where you can get help since they are mobile home heating professionals. Post to the below link under Nordyne. They are good guys and have parts if you need them . Sorry I could not be of more assistance.
Index page
|
|
 |
New Member
|
|
Jan 3, 2010, 04:55 AM
|
|
Thank you so much for your assistance.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 3, 2010, 05:30 AM
|
|
No problem
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Nordyne electric furnace
[ 1 Answers ]
I have a Nordyne 2 stage electric furnace model E1EB-015H we changed the thermostat 3 years ago using a Honeywell RTH8500D. Since this was done we have had trouble every year. I have had Technicians out each season to work on the unit and they get it working until it is time to change from heat to...
Nordyne Gas Furnace
[ 3 Answers ]
I have A Nordyne Gas furnace in my home, work up this morning to a cold house. I can't find my manual to troubleshoot the problem. Status light is blinking twice. I can get furnace to work by by-passing the pressure switch w/jumper wire. Could the problem be the Combustion blower assembly. This...
Nordyne Furnace not working
[ 27 Answers ]
Nordyne Furnace Model # L1RA 045N-08A. Blower runs constantly, whether the thermostat is on; no flame, no ignition, no heat. Have to unplug furnace to stop the blower. Red status light just steadily blinks on and off, not in a particular cadence. HELP! What do we do? Unit is still under...