    230V double pole: using one pole to also supply 115V
    Hi,

    I need to run two receptacle circuits: one 20A 230V and one 20A 115V. I was wondering if I can use one pole/hot on a double pole breaker to supply the 115V while also using it to supply the second part of the 230V. This would allow me to use one double-pole breaker and run a 12/3 to supply both circuits.

    I understand this will increase the load on the one pole and may trigger the breaker if I use both the 230V and the 115V at the same time, but is this legit? An alternative is to simply run a double0-pole 12/3 for the 230V and single-pole 12/2 for the 115V.

    Thanks,

    Steve
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 12, 2009, 04:54 AM
    Do your alternative plan.
    hpe1087's Avatar
    hpe1087 Posts: 1, Reputation: 1
    New Member
     
    #3

    Dec 12, 2009, 07:30 AM
    To answer your question... NO that is not ligit. NEC 210.4(C) states a multiwire branch circuit shall supply only line-to-neutral loads. Exception #1 states that a multiwire branch circuit can supply ony one utilization equipment. Exception #2 requires all ungrounded conductors to be opened simultaneously by the branch circuit device.

    Your circuit requirements will supply two utilization equipment loads
    sthiakos's Avatar
    sthiakos Posts: 2, Reputation: 1
    New Member
     
    #4

    Dec 13, 2009, 06:34 PM

    Thanks for the info.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring single pole thermostat in double pole fixture [ 3 Answers ]

Hello, I am trying to install a line voltage programmable thermostat into a manual thermostat fixture. The programmable thermostat is Honeywell RLV430. Instruction manual here: http://www.homedepot.ca/wcsstore/HomeDepotCanada/images/catalog/b7867367-6c05-4c82-a97c-648044b91564.pdf The...

From double pole to single pole thermostat -2 extra leads [ 3 Answers ]

The double pole thermostat for the baseboard heater has a red and a black wire coming in (from the circuit panel) and a red and a black going to the heater. The new single pole only has a red LINE lead and a black LOAD lead. If I attach red to red and then black to black, I have black (from...

Two Single Pole GFI's = one Double Pole 220v GFI? [ 6 Answers ]

Hello there, Installing a pool motor, 220v hayward northstar two speed. Could not find a double pole 40 amp GFI, electric supply store recommended two single pole 20A GFI's sharing a neutral? Does this make sense. I have a 40amp double pole in the main feeding the sub via the sub panel...

Double pole or single pole thermostat for baseboard heater [ 2 Answers ]

A more specific question here: My 240v baseboard heater says it can be wired with a single or double pole thermostat. Since 240v is already "dual pole" with two hots, do I want to stick with a double pole thermostat? Are there advantages/disadvantages to each? Thanks.

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...


View more questions Search