  • Dec 11, 2009, 10:41 PM
    sthiakos
    230V double pole: using one pole to also supply 115V
    Hi,

    I need to run two receptacle circuits: one 20A 230V and one 20A 115V. I was wondering if I can use one pole/hot on a double pole breaker to supply the 115V while also using it to supply the second part of the 230V. This would allow me to use one double-pole breaker and run a 12/3 to supply both circuits.

    I understand this will increase the load on the one pole and may trigger the breaker if I use both the 230V and the 115V at the same time, but is this legit? An alternative is to simply run a double0-pole 12/3 for the 230V and single-pole 12/2 for the 115V.

    Thanks,

    Steve
  • Dec 12, 2009, 04:54 AM
    tkrussell
    Do your alternative plan.
  • Dec 12, 2009, 07:30 AM
    hpe1087
    To answer your question... NO that is not ligit. NEC 210.4(C) states a multiwire branch circuit shall supply only line-to-neutral loads. Exception #1 states that a multiwire branch circuit can supply ony one utilization equipment. Exception #2 requires all ungrounded conductors to be opened simultaneously by the branch circuit device.

    Your circuit requirements will supply two utilization equipment loads
  • Dec 13, 2009, 06:34 PM
    sthiakos

    Thanks for the info.