    Why trane xe 1000 still running after turn off the heater
    Hello I have a Trane XE 1000 and yesterday I heard it running when the inside unit was off, I turned everything off inside and the fan in the outside unit continued to run, then I turned the break next to the unit off and finally the fan turned off. Then I turned the break on and it still continued running. After 15-20 min. passed it turned off, then it was OK. After 24 hours passed the same thing happened again. Not sure if the outside unit is overheating and maybe that is why the fan continues on. The heat inside the house is fine, if it wasn't for the fan noise we would have noticed. Help...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 28, 2009, 10:56 PM
    Could be a sticking contactor in the outside unit.
    felcars's Avatar
    felcars Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 29, 2009, 09:04 AM
    Quote Originally Posted by hvac1000 View Post
    Could be a sticking contactor in the outside unit.
    Thank you for the info, also I found a contactor but it is CTR0516 40 Amp/2 Pole/24V coil instead of CTR0516 30 Amp/2 Pole/24V coil. Can I purchase the 40 amp even though the manual says 30 amp?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Nov 29, 2009, 09:14 AM
    Does the existing contactor look like this (burned/pitted/stuck contacts)? The 40 amp rating exceeds the requirement for your unit, so that would actually be a sturdier choice than the original.
    Attached Images
      
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Nov 29, 2009, 10:07 AM
    Yes you can always use a bigger current rate contactor as long as the coil voltage is maintained at 24 volts. In fact the contacts being rated higher on the 40 amp part should out last the 30 amp one since the contacts are rated higher.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Outside unit not turning on of Trane XE 1000 [ 12 Answers ]

Ok... very new to this. I have a Trane XE 1000 and just went to turn the air conditioning on and I figured everything was fine, it sounded as if it started up OK. Went to work and when I came home the house was very hot and the vent was blowing out warm air. Checked the fuses in basement and...

Trane xe 1000 [ 1 Answers ]

Please explain why the outside unit will not stop running when unit is turned off from inside?

Trane XB 1000 [ 1 Answers ]

I came home and the unit did not run. I checked the furnace and it showed that I needed to replace the thermostat. Now that that is done, it says that the heat is fine but to call for service. Is it freon? How do I know where to troubleshoot?


View more questions Search