    Goodman Furnace Woes
    Howdy, I have a Goodman GMT070-4 Furnace that will not heat up. It did work earlier this week, but we had to cut power to the house and has since been turned back on. I don't know if the two are related.

    - The thermostat will activate the furnace blower motor, and will turn it off as well.

    I went to the attic to investigate, pulled the 2 doors off, and observed a single flash. The sticker reports this as ignition failure. I had my wife turn on the unit via the t-stat while I watched... the unit came on, red light went solid, however there were no flames nor smell of gas. There is a light switch wired to the unit, which I set to off, then back to on. The status light came back on solid, so we tried again, but still no flames or heat. If I'm correct, there is a black tube that runs up and down with three nozzles on it, and this should be the ignition area.

    I am hesitant to go any farther into it without asking for advice. The general thinking I have seen is that Goodman units are undesirable and either the gas valve is stuck, the board is shot, or the igniter tips are dirty. Any help is much appreciated.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Nov 27, 2009, 12:16 PM

    You say the electric was turned off in the house? Was the gas? Does the ignitor glow?
    xalteridemx's Avatar
    xalteridemx Posts: 8, Reputation: 1
    New Member
     
    #3

    Nov 27, 2009, 12:26 PM
    Quote Originally Posted by Joshdta View Post
    you say the electric was turned off in the house? was the gas? does the ignitor glow?
    The gas was off, but the heater did work after it was turned on.

    There is no glow from any part of the unit.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Nov 27, 2009, 01:05 PM

    If you are getting a ignition fail code, and the ignitor is not glowing I would say that you have a bad ignitor.
    xalteridemx's Avatar
    xalteridemx Posts: 8, Reputation: 1
    New Member
     
    #5

    Nov 27, 2009, 01:08 PM
    Quote Originally Posted by Joshdta View Post
    if you are getting a ignition fail code, and the ignitor is not glowing i would say that you have a bad ignitor.
    The thing is, it lists 3 other possible problems along with bad ignitor. Is there a sequence that this unit follows... such as if the gas isn't flowing the ignitor won't heat up?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #6

    Nov 27, 2009, 03:49 PM

    Vent fan, pressure switch makes, then ignitor will glow. Then a click and the gas valve should open. Furnace lights, 90 seconds blower comes on.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Nov 27, 2009, 07:56 PM
    This gadget should be glowing if ignition sequence has been activated. Observe operating sequence, listen for operating sounds from gas control.
    Attached Images
      
    xalteridemx's Avatar
    xalteridemx Posts: 8, Reputation: 1
    New Member
     
    #8

    Nov 27, 2009, 08:31 PM

    Alrighty, I'll give it another go in the morning, a bit cold up there now and a blanket will work for the time being. :)
    xalteridemx's Avatar
    xalteridemx Posts: 8, Reputation: 1
    New Member
     
    #9

    Nov 30, 2009, 05:22 PM

    OK, I had a chance to get back up there and do a full check, and here's what I observed.

    1. Activate furnace via thermostat
    2. Right side blower or fan comes on
    3. A relay click is heard around the main board area
    4. A noise that sounds like gas flow comes on for about 5 seconds then shuts off.
    5. Wait about 20-30 seconds, relay click is heard again.
    6. Repeat steps 4 and 5 two more times.
    7. Status light blinks to indicate ignition failure.

    The large left blower that looks like it would feed heat to the house never comes on at any point. I found the igniter and two small push button switches. The switches seemed to be OK, but the igniter never started to glow. It is covered in carbon or just burnt.

    Is this the source of the problem?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #10

    Nov 30, 2009, 06:12 PM
    It could be a defective ignitor. You can test this item by attaching a volt meter to the two leeds that go to it. Then reactivate the furnace and watch the meter for a voltage reading. Post back with results. BTW you will have to be looking at the meter when the furnace is activated or you might miss the voltage reading since the circuit board only supplys voltage to the ignitor for a small amount of time. Also if you need to replace the ignitor also clean the flame sendor with steel wool or sandpaper to be sure it is functional.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #11

    Nov 30, 2009, 06:55 PM

    Based on your description of your observations, either the ignitor has failed (more likely) or the circuit board is failing to power the ignitor (less likely).
    xalteridemx's Avatar
    xalteridemx Posts: 8, Reputation: 1
    New Member
     
    #12

    Dec 3, 2009, 05:22 PM

    Well, tomorrow it's going to snow in Houston and I couldn't find the part locally that would sell to someone that isn't a dealer. Any tips on where to find this part?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #13

    Dec 3, 2009, 06:45 PM
    Try furnaceparts.com, may be a kit like this. #0230K00001.
    Attached Images
     
    xalteridemx's Avatar
    xalteridemx Posts: 8, Reputation: 1
    New Member
     
    #14

    Dec 10, 2009, 08:28 PM

    KC13 -

    I acquired the conversion kit on the net for ~$25. It just so happens that one of my co-workers worked for Goodman for 18 years and he offered to take a look at my problem.

    The igniter had a hairline fracture in it.

    Replaced it, and I now have heat in my home. Many thanks to all that helped and offered advice.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #15

    Dec 11, 2009, 12:37 AM
    Glad you got it going
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #16

    Dec 11, 2009, 04:01 AM

    Bravo!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace gmp [ 7 Answers ]

Ok. I can turn the thermostat to 72 and it will stay on 64 with the fan blowing constant. Burners aren't firing. On the control board for the furnace, there is a trouble shooting light that blinks to tell you what is wrong. It blinks four times which indicates an "Open Limit Switch", and it tells...

Goodman furnace GMNT080-4 furnace runs good for a while then has to be manually reset [ 5 Answers ]

I have a Goodman GMNT080-4 (90%). I'm having the same problem As Streatherg did back in the Nov 2006 question. I reviewed his article and tried Every thing on there but seems to be doing the same thing. The furnace kicks on for about an hour then locks out and has to be manually reset threw...

Old furnace woes [ 1 Answers ]

First of all thanks for quick response Do I use sand paper to clean pilot orifice? And where is the thermocouple located and are they universal? Thanks again

Old furnace woes [ 1 Answers ]

I have a 30 year old furnace (coleman) in my mobile home It has a screw off cap to light pilot When I open it it has a strong draft pulling through the furnace But when I do get the pilot lit and get the thing fired up it will not stay lit (the main burner) for too long, some times it works...

Carrier furnace woes [ 5 Answers ]

Hello, my name is Steve and I have a carrier 58PAV111 electronic ignition furnace that is giving me grief! The story... burners shut down and blower continues to run. LED code is 13. If we shut down power and let it sit for 5 minutes (as the instructions say) it will reset and run just fine or a...


View more questions Search