    Blower motor won't shut off on bryant
    Have a bryant furnace 20+ yrs old blower motor won't shut off even after desired temp. is achieved. New thermostat.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 22, 2009, 09:37 PM
    At the furnace remove the green wire on the G terminal. If the fan turns off when the heat cycle is finished then it is a thermostat wiring problem. NOTE also make sure the new thermostat is not set to fan on but to fan automatic.
    tman1's Avatar
    tman1 Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 22, 2009, 11:11 PM
    Quote Originally Posted by hvac1000 View Post
    At the furnace remove the green wire on the G terminal. If the fan turns off when the heat cycle is finished then it is a thermostat wiring problem. NOTE also make sure the new thermostat is not set to fan on but to fan automatic.
    Ty for advice checked setting on thermo. And did as advised but no luck
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 22, 2009, 11:49 PM
    Then the fan/limit control is defective or the fan relay is stuck/defective.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Nov 23, 2009, 03:51 AM
    Model #? If the unit doesn't have one of these, the circuit board is the problem.
    Attached Images
      
    tman1's Avatar
    tman1 Posts: 3, Reputation: 1
    New Member
     
    #6

    Nov 24, 2009, 04:00 PM

    It was the circuit board Thanks to both of you for your time and suggestions

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant 373LAV Furnace - Blower will not shut off [ 7 Answers ]

Good afternoon all, My question is in regards to the Bryant 373LAV Downflow/Horizontal gas furnace. A good friend of mine called for my help because about a month ago, her furnace blower randomly began running all the time and the only way she could shut it off was to flip the breaker on the...

Blower motor won't shut off in attic [ 4 Answers ]

How do you fix a fan motor that does not shut off at the furance and what do you normally shut the fan limted switch too I know if I go up there and turn fan limted switch it will shut off and the theromstate and fan motor have to be set togather this old unit but heat great beside this problem it...

Blower motor won't shut off in heat mode but works fine in A/C mode [ 0 Answers ]

I have an older lennox unit that is pilot light. The blower motor won't shut off when the temp is reached on the thermostat but it works fine in ac mode. What could cause this? I'm confused because it worked 2 weeks ago when I turned my ac off and the thermostat is in auto and only shuts off when I...

State Water Heater Blower Motor won't shut off-Fix [ 1 Answers ]

In response to those with the above problem, I was running downstairs all the time to tap on the blower control switch locatedin front of the gas valve,and it was driving me nuts. I inserted a piece of aluminum foil between the switch and the metal pole it slides in on. I have cycled the water...

Blower does not shut off on 15 yr old Bryant heating unit [ 2 Answers ]

The blower on my 12-15 yr old Bryant keeps going ignoring the t-stat stetting. I taught it was the t-stat, I replaced it and it still does the same thing. About a year ago the board was replaced with a newer one that has a fuse (3 amps) And was told that with the fuse it would prevent it from...


View more questions Search