Have a bryant furnace 20+ yrs old blower motor won't shut off even after desired temp. is achieved. New thermostat.
![]() |
Have a bryant furnace 20+ yrs old blower motor won't shut off even after desired temp. is achieved. New thermostat.
At the furnace remove the green wire on the G terminal. If the fan turns off when the heat cycle is finished then it is a thermostat wiring problem. NOTE also make sure the new thermostat is not set to fan on but to fan automatic.
Then the fan/limit control is defective or the fan relay is stuck/defective.
Model #? If the unit doesn't have one of these, the circuit board is the problem.
It was the circuit board Thanks to both of you for your time and suggestions