Ask Experts Questions for FREE Help !
Ask
    pm_hardikar's Avatar
    pm_hardikar Posts: 2, Reputation: 1
    New Member
     
    #1

    Nov 6, 2009, 08:21 AM
    5 HP 3 P wire and CB sizing

    I have a 5 HP, 3 ph DOL started motor driving an air blower. The motor is situated at approx 50 mtrs from the nearest DB . Could you tell me the cable size and nos, type, rating, breaking capacity and the locations of MCBs in the motor circuit starting from the DB?

    <moved from Electrical Engineering and into it's own thread>
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 6, 2009, 11:28 AM
    What does DOL stand for? Across the Line?

    Need to know voltage to detemine amp draw, to size the branch circuit size, overcurrent and overload size.

    What country are you located?

    What does this mean:

    and the locations of MCBs in the motor circuit starting from the DB?
    pm_hardikar's Avatar
    pm_hardikar Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 7, 2009, 02:06 AM

    DOL stands for Direct On Line( full voltage) starting.
    I belong to India. The voltage is 415 v, 3 ph,
    50Hz.
    Location of the MCB means starting from the distribution board up to the motor( distance 50 mtrs) how many MCBs I need to put in series and at which places? I want to totally eliminate fuses and Isolators.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 7, 2009, 05:07 AM
    You will need to check local codes or regulations to size the branch circuit and what type of cable, and the nameplate of the motor for actual amps but a 5 HP 415 VAC 3 Ph motor should draw about 7 amps.

    Local code will tell you the derating factor. Here in USA we take full load amps and increase by 25% to size branch circuit size.

    You are probably under IEE regulations, some help can be found here:

    http://www.tlc-direct.co.uk/Book/3.6.4.htm

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Sub-panel sizing of wire [ 3 Answers ]

Have an existing 100 amp service. Wish to install a 70 amp sub-panel. What size wire should be used? Distance to sub-panel is 45 feet.

Wire Sizing [ 2 Answers ]

I am rewiring a house in Mexico and following the 2002 NEC for wire sizing, grounding, circuits, etc for all work from the meter on. Service panel is 125A and will support air condition along with all other lighting and appliances. The utility company will only supply a 6 AWG overhead triplex...

Sizing Wire [ 3 Answers ]

Im running a new 100amp sub about 40 ft from house. Ive been reading but wanted to know you guys' opinion. Should I go with THWN #3 for my Hots/Neutrals. And #8 for EQ Gnd.? I'm kind of confused about the 90/75 degrees that rate this type wire. Also I understand about having to conduit...

Wire sizing for sub panel. [ 1 Answers ]

Thank you for the response on my sub panel questions. I finally found a slim line breaker which will work in my main panel. I can now consolidate two breakers to give me room for a 100 ap breaker. This breaker will feed the sub panel in my workshop. I plan on placing a 100 amp sub panel in the...


View more questions Search