    30amp 10-2 wire to sub panel
    I want to run a 30 amp breaker to a sub panel in my shed. That will run a couple of outlets shop light and a 20amp exhaust fan. The run is 150ft. Will that work?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Nov 5, 2009, 10:42 PM
    NOPE. Consider a 40 amp circuit to the sub panel. You will need 4 wires, 3 #6 and 1 #8 for the ground. You will also need a grounding rod. Have you done this type of work before?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Nov 6, 2009, 04:32 AM
    A 30A feeder is the minimum size you can run, so #10 is OK if the bare minimum is OK for you. Thing is, 10/2 is NOT OK. You would need 10/3 to have a 120/240v sub-panel.
    A 120v only panel is technically code legal but makes absolutely no sense to install.

    Like Missouri said, a grounding electrode (ground rod) is required in any detached building with a sub-panel.
    jakejosh12's Avatar
    jakejosh12 Posts: 2, Reputation: 1
    New Member
     
    #4

    Nov 6, 2009, 04:35 AM

    I have done some but not to a sub panel so you are saying I need #6 wire and #8? Why so big because of the run? Thanks For the last answer
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Nov 6, 2009, 05:32 AM
    Correct, the #10 will result in too high a voltage drop for a 150 foot run.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting neutral wire to ground wire in breaker panel [ 3 Answers ]

Can the neutral wire be connected to the ground wire at the neutral bar in the breaker panel?

How do I add a 30amp to my circuit panel [ 3 Answers ]

How do I determine the size of my circuit panel. I want to add a 30amp plug socket for my RV hookup.

Sub Panel Wire [ 2 Answers ]

I recently did a walkthrough with the electrician who is helping me get my basement wired up. During that time I believe he had told me to pick up approximately 10ft of 4/4/2 electrical wire to run a 100A Breaker from my 200A panel to a 100A sub panel. Another guy told me I should get 4/3 wire...

Connecting 3 wire to a 4 wire service panel [ 5 Answers ]

I am trying to connect from a 3 wire system at the utility pole to a 4 wire service panel inside a new mobile home. I called an electrician for some advice and was told that I needed to drive an 8ft ground stake and attach a solid copper wire from the stake to the ground bar in the panel. Then I...

3 wire to 4 wire from sub panel to receptacle [ 1 Answers ]

I am installing a new stove and running new romex from the box to the stove. How do I properly connect the 4 wires at the box that currently has only 3 wires so that the new system is grounded? Saw this above and it is similar to my question earlier, with the response being "yes" as to the box...


View more questions Search