    Service amperage
    I am stumped on this I need to now the total net load and the total load service for a 1800 square foot home with 11 kW range and a 6 kW 240 V dryer I have looked at the back of the NEC and I need to check my answers thank for any help?:mad:
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 10, 2007, 03:58 AM
    Assuming no heat or AC, I arrive at 80.89 amps.

    The range only needs to be calculated at 8Kw.

    The dryer at 6Kw.

    3 watts per square foot x 1800 SqFt=5400 watts+3000w small appliance+1500 laundry.

    First 3000 watts at 100% plus the remaining at 35%+8Kw+6Kw/ 240 volts=80.89 amps
    djelbachatu's Avatar
    djelbachatu Posts: 1, Reputation: 1
    New Member
     
    #3

    Nov 4, 2009, 09:06 PM

    What is the minimum number of 120-volt, 2 wire branch circuit that would be required for this home?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 5, 2009, 03:52 AM
    3 watts per square foot x 1800 SqFt = 5400 watts/120 volts = 45 amps / 15 amps per circuit = minimum of 3 -15 amp general purpose lighting circuits.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Nov 5, 2009, 07:30 AM

    The keyword is TK's last post is "Minimum".

    You can put more circuits in to meet your needs, but you cannot put less then 3 circuits.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Amperage capacity [ 3 Answers ]

Upgraded our circuit breaker to 20 amps for each slot. Is it possible/ safe to use one slot (20 amps capacity) for light bulbs and a garage door motor? The breakdown are as follows: Kitchen > 4 fluorescent bulbs 40 watts ea. Dining > 1 30 watts curcular bulb with ceiling...

Breaker amperage [ 1 Answers ]

What amp breakers are typiclly used in residential for dryer , washer, dishwasher, glass cooktop, separate oven, 4 ton package unit, bath gfi, etc?

Amperage meter [ 5 Answers ]

I have older amperage meter form Micronta, I am thinking 1960's. I don't know how exactly to use it. It comes with the two needle probes and looks like the dial settings are like those on more modern versions, I am not electrically inclined and don't know the settings for testing live voltages or...

Circuit amperage [ 2 Answers ]

If I have a 15 amp circuit does that mean I can only run one 15 amp rate device on that circuit? Or can I run any number of 15 amp or even higher amp devices, with wattage being the criterion for not overloading the circuit?

150 Amp Service Adding more Amperage [ 1 Answers ]

The house we are looking at to buy has a 150 AMp Main breaker box. Can this be replaced with a 200 Amp box to give additional capacity in terms of load? I am planning to build a workshop that will have a 50 AMP sub panel to provide 30 AMP 220 and several 20 AMP 110 circuits