    Blower comes on intermittently in cool down cycle
    I have a coleman gas furnace manufactured in the mid 70's. The blower seems to malfunction during the cool down cycle. It runs for a while and cooks down the unut, then switches off, then back on for a few minutes (15 min). Then stayes off like normal until the next time the burners come back on. I suspect the fan relay may be going bad, but am not sure if the limit switch would have anything to do with this . Can someone give a novice a little insight please ? How do i check this ? Thank you...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 1, 2009, 01:15 PM
    Your unit is reacting to residual heat left in the combustion chamber/heat exchanger. This is usually caused by the blower fan control going out of range or a dirty evaporator traping the heat in the unit. There is a wiring diagram on the unit somewhere to help you locate your control.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #3

    Nov 1, 2009, 09:54 PM
    Apply this highly-scientific formula: 35 years (give or take a couple) x number of days per heating season x number of heating cycles per day = 1 worn-out fan control!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant Plus 90 blower runs intermittently [ 7 Answers ]

I have a Bryant 90 Plus (350 MAV) gas furnace that is about 13 years old with an intermittent problem. The inducer motor starts, igniter lights, gas valve opens, and burner lights and runs but occasionally the blower motor will not start. When this occurs the plenum attached to the furnace gets...

Blower Fan on gas Comfortmaker RPG Heat Exchanger runs intermittently [ 3 Answers ]

Hello, I'm new here, and I've been reading a lot (well, 4 or 5 pages anyway) of what's already been asked, and I haven't found my specific problem... yet. This gas hot air furnace was installed circa 1987? So, Here's what's happening. (I actually timed these cycles with a second-hand.) Turn...

Airhandler (inside blower) works intermittently [ 5 Answers ]

Help! Please I recently changed my heat pump capacitor after fan stopped working. Two days later, blower to inside unit stopped. After turing off all the breakers (i.e heat pump and inside blower motor, etc.) it worked for two days. Then I changed capacitor to air handler unit, thinking this...

Blower motor intermittently struggles to come on [ 1 Answers ]

Hey Folks I know this a rather common issue, but there are several variations on it that make me unsure which way to turn. I have a Bryant furnace (6 years old) and the original blower motor was replaced, along with the fan wheel, about 2 years ago. Now I get this intermittent issue of it not...

Blower works intermittently for A/C [ 1 Answers ]

I have an old York furnace with central air. When turning on the A/C, sometimes the blower comes on, sometimes it doesn't, and sometimes it toggles off and on with a loud clicking sound. If I use the manual switch on the limit control, everything is fine, but of course, then the blower is on...


View more questions Search