    THHN1 8 gage wire for 50 amp circuit. Is this OK?
    I am wiring a hot tub and installed a new 50 amp circuit. I have 6 gage wire (35 feet) from the panel to the outer wall of my house. From there I am preparing to run 95 feet of THHN1 8 gage wire that I will be burying 18" under ground in grey schedule 40 pvc.

    Two questions.

    Is 8 gage THHN1 wire appropriate for the 50 amp circuit?

    Is 95 feet too long of a run for the 8 gage THHN1 wire (as far as power loss over distance goes)?

    Thank you
    Jhub65's Avatar
    Jhub65 Posts: 7, Reputation: 1
    New Member
     
    #2

    Oct 17, 2009, 07:22 PM

    Just for clarification, the 6 gage wire I am running (35 feet) from my panel, is 6/3 wire.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Oct 17, 2009, 08:53 PM

    You really have to run #6 and you have to use THWN or THHN/THWN dual rated wire. You can use a #10 insulated ground. So you need three #6 and one #10.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Oct 18, 2009, 04:44 AM
    #8 THHN/THWN wire in conduit is perfectly fine for a 50A circuit. However, the instructions may specifically state to use #6, so check that first. Also check that they do or do not require a larger ground. Many do.
    In any case the ground MUST be insulated once the circuit leaves the structure.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Oct 18, 2009, 08:26 AM

    That's at 135 (100+35) feet @ 50A. Don't think so. #6 at 135 feet give a 2.5% drop in voltage at 240 V.

    #8 at 100' 240 V gives a 3.3% (7.8 V) drop, not including the 35' (2.7%) or 1.1 Volts. Total drop 7.8+1.1 = 8.9V is 3.7% which is higher than 3%.

    Motors are involved too.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Oct 18, 2009, 04:12 PM
    A) 130' run (95+35)
    B) 40 amps, not 50. The circuit is 50A, the load is likely 40 or under.
    C) The run is partially #6.
    D) Voltage drop is a suggestion, NOT a code requirement. Especially the 3% figure. 5% total is FINE.

    Anyway,
    All #8, @ 130', @ 40A, @ 240v = 3.3% drop.
    This is perfectly acceptable, especially considering the section of #6 that is being used.

    I am not saying #6 is wrong, it certainly is not, but it is not mandatory.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Using the proper gage wire fro long distance outside run [ 3 Answers ]

Hi, 1) I am looking to run a 460' wire to an 5-wheel trailer - which I understand needs a 30 amp circuit. For the AC particularly, and need to figure out what is the proper gage wire to use.:confused: 2) Also, I am told that I can not run romex wires in a conduit outside, is that true?:mad: ...

Proper wire gage [ 1 Answers ]

Currently my sub panel in the garage is supplied by 10 gage 2 wire with ground from a 30 amp dbl pull breaker in the house. The run is 30' to the 100 amp box in the garage. The garage is a part time workshop with several power tools on at the same time along with 10 4' fluorescent light fixtures...

How to wire 2 wire fan remote to 3 wire circuit? [ 10 Answers ]

I have a room that has 2 light switchs to the same light, so it is a 3 wire circuit. I bought a fan with a remote and the wall mounted remote has only 2 wires, how can I connect it? Thanks, Pete

12 Gage wire 110 outlet [ 1 Answers ]

What amp breaker should I use for a out side 110 outlet using 12 gage wire.Used for plugging in vacuum cleaner to clean cars.

12 gage wire on a 15 amp switch [ 1 Answers ]

If you can use 15 amp receptacles and switches on a 20 amp circuit, then why won't they accept (quick connect) 12 gage wiring?


View more questions Search