    reprosser's Avatar
    reprosser Posts: 2, Reputation: 1
    New Member
     
    #1

    Oct 6, 2009, 02:13 PM
    Components for Power pole for Well
    I need to buld a power pole for a well that will be drilled. I already have a pole to use.

    I know I need the weather head, conduit to meter box, conduit to breaker box, conduit to underground, and ground rods.

    What I cannot seem to find is a 100A outdoor breaker panel with a main breaker and a few spaces for breakers. All I can find is a 100A "Main Lug". This does not have a main breaker.

    Can I add a Main Breaker to a Main Lug? Will I have to put some disconnect switch between meter an Main Lug.

    I only need to run the well pump (220) and maybe a light switch (110).
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 7, 2009, 03:00 AM
    If you go to an electrical distributor, they can find a NEMA 3R Raintight Panel with a main breaker and branch breaker slots. These are very common, more than you may realize.

    Every brand of panelboard makes them, just not sure what brand is sold in your area.

    Here is one found at Grainger's:
    Load Center,Outdoor,100 A - Panel Boards - Distribution - Electrical : Grainger Industrial Supply
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Oct 7, 2009, 05:45 AM

    Not what you ask but, why would you want 100 amps at a well pole. Twenty amps for pump and 20 for auxiliary should be all you could use? Just asking.
    reprosser's Avatar
    reprosser Posts: 2, Reputation: 1
    New Member
     
    #4

    Oct 7, 2009, 09:56 AM
    The Grainger box is what I was looking for - except it has way more spaces than I need. Cannot find them at Lowe's, or Home Depot. Guess I am looking in the wrong places.

    This will be a 60 amp service, and I had not heard of a 60 amp box with main breaker - or a 40A.

    I really would like the simplest, cheapest solution since it is just for a well pump.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #5

    Oct 7, 2009, 10:12 AM

    TK

    Does he need a main breaker? Seems to me that all he would need is a 40 amp/4 space water proof disconnect box.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Oct 8, 2009, 02:50 AM
    Beats me what is needed, just trying to answer the questions as given.

    Panels come in various sizes of branch circuits, 2, 4, 6, 8, 10, 12 and so on.

    A 12 circuit Main Lug Only NEMA 3 R can be used, for instance, with two circuits used a 2 pole 60 Amp, backfeed with the incoming lines, use a retainer kit since this breaker will be the Main. This would leave 10 poles for branch circuits.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting Power Source to 3 Single Pole switch(s) [ 8 Answers ]

:confused:I am building a stand alone garage and I am doing the basic wiring myself. The 3 switch(s) are beside a walk through door on the other side of the building from the panel box. How can I limit the number of source feeds from across the room? One switch controls the two fluorescent ceiling...

Need power pole moved [ 1 Answers ]

How can I get a power pole moved, It is where I want to build Thanks

Power pole that electric company won't fix. [ 3 Answers ]

So I'm helping my friend with this problem. He lives on a lot with a private power pole. Recently it shifted and the meter (which is on the pole) disconnected from the breaker that feeds into his house. So now he is without power, I've contacted a contractor to set the pole straight, but he said...

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...

Temporary Power Pole [ 2 Answers ]

I recently bought a lot and put up a temporary power pole. I installed a 200 amp meter box with a Siemens 200 amp main breaker panel. I plan on camping with my Pop-up (30 amps), and also want a separate 20 amp circuit. Since I don't have a footprint for a future house yet, I had to apply for a...


View more questions Search