Ask Experts Questions for FREE Help !
Ask
    portangeles's Avatar
    portangeles Posts: 3, Reputation: 1
    New Member
     
    #1

    Oct 4, 2009, 07:36 PM
    Arc fault circuit
    For a bedroom with 5 recessed lights (I will use 26 watt compact fluorescence lights) 8 wall outlets, and a ceiling fan is one 20 amp circuit with an arc fault breaker sufficient, and code compliant? I had planned on two circuits, one 15 amp circuit for the lights and one 20 amp circuit for the rest but thought it reasonable to just use one circuit due to the high cost of arc fault breakers. I am concerned that the inspector won't consider my recessed lighting at 26 watts each since someone else could put 100 watt incandescence lights in them.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Oct 4, 2009, 08:48 PM

    This Electrical Wiring in the Home: Arc Fault Breaker Trouble, arc fault breakers, arc fault breaker

    Indicates that ARC faults are not required for lighting and could be troublesome.

    EDIT: NEC 210.12B Arc Fault for receptacles only

    PS: Go to Link Electrical & Lighting top left; Find the sticky on how to read the NEC online
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Oct 5, 2009, 02:44 AM
    Kiss, you are mis-reading Section 210.12 B. It states all "outlets" in those areas shall be arc fault protected.

    It does not say receptacles only.

    Check the definition of "outlet", you will find that a light fixture is a "outlet", and I quote, " A point on the wiring system at which current is taken to supply utilization equipment."

    Even a smoke detector, per NEC, needs AFCI protection. Some states waive this requirement.

    A light fixture in a bedroom needs AFCI protection.

    Port, your circuit as described is fine. Check your local code on the smoke detector issue. You did plan to have a hardwired interconnected smoke detector in each bedroom and one in the hall way, correct?
    portangeles's Avatar
    portangeles Posts: 3, Reputation: 1
    New Member
     
    #4

    Oct 7, 2009, 10:54 AM

    According to the electrician at Home Depot the arc fault is required for lights as well as receptacles in a bedroom but not allowed for the smoke alarm. So I am going with the one circuit per bedroom plan.

    Thanks for the help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Oct 8, 2009, 02:52 AM
    Do me a favor, check with local code, and not a clerk at a hardware store, UNLESS that clerk has a license for that trade.
    portangeles's Avatar
    portangeles Posts: 3, Reputation: 1
    New Member
     
    #6

    Oct 9, 2009, 09:38 PM

    Good point. He is a licensed electrician. The clerk called him over to answer my question.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Arc-Fault Circuit [ 1 Answers ]

In a commercial building, namely a fire house, with sleeping quarters, do the circuits in those rooms need to be arc fault protected.

Ark fault circuit interrupter [ 1 Answers ]

Can an afci be put on a circuit with no grounds or one that is sharing neutrals with another cicuit

Arc Fault Circuit [ 3 Answers ]

Hello, Only when using my portable generator, the arc fault circuit (for Master Bedroom) keeps tripping.. Do I have to do anything extra?? Details: Coleman powermate 5kw Maxa ER Plus (pm0525312.17) Using the L14-20 receptical with Floating Neutral 10/3 W/ground Bus Drop cable (35 ft) to...

Arc Fault circuit [ 2 Answers ]

I have a 3-wire home run to the panel which supplies 2 circuits. One of the circuits supplies a bedroom and I want to comply with the arc-fault breaker protection rule. Square D indicates the common neutral will cause the arc-fault to trip. Is there a solution to this? Bob

Arc fault circuit breaker [ 5 Answers ]

I am in a high rise condo building. My bedrooms(2) arc fault circuit breaker (1) seems to be in off position (the 15amp switch) after the power in my 2 bedrooms went out quietly during the day. However, I cannot move the 15 amp switch back to the 'on' position. What is the likely problem?


View more questions Search