    changing tstat from Honeywell T841A1712 with Lennox T8611g
    PLEASE need help-would like to change thermostat on my American Standard model WYC060F100AA heat pump. Current wiring on Honeywell T841A1712 thermostat is:

    ZONE 1 THERMOSTAT
    X- BLACK WIRE----COMMON
    R- RED WIRE-------HOT
    G- GREEN WIRE---FAN
    W2-WHITE WIRE--2ND STAGE HEAT
    B-BLUE WIRE------HEATING MODE
    E-BROWN WIRE---EMERGENCY HEAT
    Y-YELLOW WIRE---EQUIPMENT CALL
    O-ORANGE WIRE--COOLING MODE

    ZONE 2 THERMOSTAT
    W1-WHITE WIRE------HEAT
    RC-RED WIRE-----------HOT
    RH-BLACK WIRE JUMPER TO RH
    Y1-YELLOW WIRE-----COOL

    ZONE 1 DAMPER
    M1-RED WIRE
    M2-WHITE WIRE
    M4 BLUE WIRE

    ZONE 2 DAMPER
    M1-ORANGE WIRE
    M2-YELLOW WIRE
    M4-BLACK WIRE

    TERMINAL CONNECTION INSIDE HEAT PUMP
    COMMON-C-BLUE WIRE
    HOT-R- RED WIRE
    COMPRESSOR-Y- YELLOW WIRE
    FAN-G- GREEN WIRE
    CHANGEOVER VALUE(HEAT)-B-NOT USED
    CHANGEOVER VALUE (COOL)-O-ORANGE WIRE
    2ND STAGE HEAT-W2-BLACK & WHITE WIRE
    2ND STAGE COOL-Y2-NOT USED
    --------------------------------------------------------------------
    24 VAC 40VA (1)-RED WIRE
    POWER SUPPLY(2)-BLACK WIRE
    ----------------------------------------------------------------------
    ZONE 1 THERMOSTAT
    COMMON-CX-BLACK WIRE
    HOT-R-RED WIRE
    EQUIPMENT CALL-Y-YELLOW WIRE
    FAN-G- GREEN WIRE
    HEATING MODE -B-BLUE WIRE
    COOLING MODE-O-ORANGE WIRE
    EMERGENCY HEAT-E-BROWN WIRE
    2ND STAGE HEAT-W2-WHITE WIRE
    2ND STAGE COOL-Y2-NOT USED


    New thermostat Lennox T8611G has: R,C,Y,B,L,X1,X2,G,E,W2 & O
    QUESTION? Should my connect be :
    OLD TSTAT-----------------------------NEW TSTAT
    X-BLACK WIRE------:confused:----------- C- BLACK WIRE
    R- RED WIRE------------------------- R- RED WIRE
    G- GREEN WIRE---------------------- G- GREEN WIRE
    W2- WHITE WIRE---------------------- W2- WHITE WIRE
    B-BLUE WIRE--------:confused:------- X- BLUE WIRE
    E- BROWN WIRE--------------------- E- BROWN WIRE
    Y- YELLOW WIRE -------------------- Y- YELLOW WIRE
    O- ORANGE WIRE-------------------- O- ORANGE WIRE

    Would like to do away with ZONE 2 THERMOSTAT because area it is used in is just one open loaf that is open to great room. How do I go about this change? And making sure that damper is opening with ZONE 1 DAMPER
    Thank you in advance for any and all assistance with this task!
    Charles
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Aug 16, 2009, 10:27 PM
    Hello Charles. You have just walked into a hornets nest. STOP what you are doing and reconsider this.

    First it takes a seasoned professional to figure out most zoning systems and yours is compounded by the fact that it is a heat pump.

    Second is the fact that you have three wire dampers and they can be stinkers to work with. These work with a common wire and power wires for both open and closing. Usually the brand is Trol-A-Temp by Honeywell.

    Third and most important is a warning about the magic smoke. All it takes is one wire located to the wrong connection and your system will let out the magic smoke. If this happens be ready for a HUGE repair bill since most of the controls and wiring will be destroyed.

    Since I am not there to actually oversee the situation and since trying to do this on a message board is just about impossible I am passing on the above information.

    That is not to say that you may get lucky and all works correctly when you are done but personally I want no part of this since my past experiences with message boards have left me with the conclusions above. I have personally wired many zoning systems and most were far more complex than the one you have but I had a advantage of having all the control circuits,equipment details etc on site while doing the work. This type of work is hard to do by remote control if you know what I mean.

    I wish you good luck in your endeavors and here are a few links to some of your zoning toys.

    http://www.bayareaservice.com/Manual..._prod_data.pdf

    http://www.bayareaservice.com/Manual..._prod_data.pdf

    http://www.bayareaservice.com/Manual...all_manual.pdf
    cchav61590's Avatar
    cchav61590 Posts: 19, Reputation: 1
    New Member
     
    #3

    Aug 17, 2009, 05:41 AM
    [QUOTE=hvac1000;1928331]Hello Charles. You have just walked into a hornets nest. STOP what you are doing and reconsider this.

    Good thing I looked before I leaped,especially when there is a hornets nest with magic smoke at the bottom. Thank you for your answer.. Question can I leave system as is and add new thermostat in place of old thermostat 1.
    New thermostat Lennox T8611G has: R,C,Y,B,L,X1,X2,G,E,W2 & O
    QUESTION? Should my connect be :
    OLD TSTAT-----------------------------NEW TSTAT
    X-BLACK WIRE----------------- C- BLACK WIRE
    R- RED WIRE------------------------- R- RED WIRE
    G- GREEN WIRE---------------------- G- GREEN WIRE
    W2- WHITE WIRE---------------------- W2- WHITE WIRE
    B-BLUE WIRE--------------- X- BLUE WIRE
    E- BROWN WIRE--------------------- E- BROWN WIRE
    Y- YELLOW WIRE -------------------- Y- YELLOW WIRE
    O- ORANGE WIRE-------------------- O- ORANGE WIRE
    Will this work?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Aug 17, 2009, 06:17 AM
    While it is possible to do that my warning still stands. When you are dealing with the type of system you have sometimes the wiring will just not work out.

    As long as X is common for sure and

    B is first stage heat it might work BUT

    These terminals might work the dampers or other relays or end switches. This is something we do not know. If you really have to do it at your own peril.
    cchav61590's Avatar
    cchav61590 Posts: 19, Reputation: 1
    New Member
     
    #5

    Aug 17, 2009, 06:23 AM
    [QUOTE=hvac1000;1928765]While it is possible to do that my warning still stands. When you are dealing with the type of system you have sometimes the wiring will just not work out.
    Thanks again: I will take your advice and hire a pro because the risk is not worth the gain.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Aug 17, 2009, 08:37 AM
    Smart move. This way if they mess it up they get to fix it for free.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Changing tstat from Honeywell T841A1712 with Lennox T8611g [ 2 Answers ]

PLEASE need help-would like to change thermostat on my American Standard model WYC060F100AA heat pump. Current wiring on Honeywell T841A1712 thermostat is: X- BLACK WIRE R- RED WIRE G- GREEN WIRE W2-WHTE WIRE B-BLUE WIRE E-BROWN WIRE Y-YELLOW WIRE O-ORANGE WIRE

Honeywell to Hunter tstat [ 6 Answers ]

I am wanting to replace my old Honeywell Chromotherm III to a Hunter Set & Save 44260. The wiring from the old is: W-white, G-green, C-blue, R-red, Y-yellow and orange is not connected (O,W,G,C,R,Rc,B,Y). My new one is labeled G,RC,RH,Y/O,W/B & Y1 with RC & RH jumped. I have gone through most of...

Honeywell tstat with aux heat [ 3 Answers ]

I have a new luxaire heat pump with aux heat. I am replacing the tstat. Is the supposed to be a wire for the aux slot? I have the red on the r/rc, the blue on the c, the yellow on the y, the green on the g and the white & orange together on the o/b. any ideas are welome. Thanks Gretchen ...

Upgrading to a Honeywell TH8320 tstat [ 1 Answers ]

I recently purchased a Honeywell TH8320 programmable thermostat to bring a little energy efficiency to my new home. I have a Carrier 25HBA3 Base Series split system pump with a unit outside, and one indoors (installed up in the attic space above my garage). I detached the previous thermostat and...

Converting from Honeywell LR69071 to Honeywell T8611G [ 1 Answers ]

I have a Honeywell LR60971 with these connections: R Red X Blu G Grn Y Yel O Org W W2 B Blk E Brn


View more questions Search