    Wire sizing for 250 feet service
    I'm running an underground electrical service (240 volt) from the meter to the house, 250 feet. What would the wire size be and the size of the conduit? The main panel will be 200 amps. I would like to get a price for both aluminum and copper.
    Thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jul 23, 2009, 10:15 PM

    You don't necessarily have to use conduit, but it needs to be put deeper, like 36". The utility governs these regulations and they may require their own wire or may require that they burry it.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jul 23, 2009, 10:29 PM
    At least 250 kCmil for 2.2% voltage drop with a #4 grounding conductor for copper.

    At least 350 kCmil for a 2.5% voltage drop for aluminum with a #2 grounding conductor.

    Wire type may modify these a bit. Wire type influences conduit sie.

    Here is an example for a utility's require,ents.

    http://www.nipsco.nisource.com/elecstd/er/er19270.pdf
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jul 24, 2009, 04:54 AM
    Services are sized differently the branch circuits. We do not use the same method for figuring voltage drop for both.
    For instance, we would not use 200A if we needed to figure voltage drop for a 200A service.

    Also, service conductors are sized smaller that typical branch circuits.

    The utility in my area would recommend "standard" sized cable for up to 250'. Beyond that they would recommend up sizing.

    For up to 250' I would use 2" PVC, and 4/0, 4/0, 2/0 AL conductors, or 2/0, 2/0, 1/0 CU conductors.
    Beyond that I would bump up to 250mcm AL.
    RJWalt's Avatar
    RJWalt Posts: 2, Reputation: 1
    New Member
     
    #5

    Aug 2, 2009, 05:25 PM
    Let me give you another option. Could I run an underground service (220 volt) from the utility pole at the roadway to a cabin about 600 feet away, instead of the utility company running overhead wires halfway or is that to big of a run. I wanted to put in a 200 amp circuit panel, however the needs of the cabin doesn't require that big of panel. I was looking at running 400 kcmil in conduit. Also would that wire be possible to pull by hand?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Aug 3, 2009, 02:46 AM
    400 MCM would do the trick.

    Many hands would be needed to pull this run.

    More than likely will need a truck or a wire puller to pull this.

    Be sure to use steel elbows if your using PVC conduit. PVC sweeps will melt from the friction of pulling long runs.

    Do yourself a favor and use min 4 inch conduit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Wire Sizing [ 2 Answers ]

I am rewiring a house in Mexico and following the 2002 NEC for wire sizing, grounding, circuits, etc for all work from the meter on. Service panel is 125A and will support air condition along with all other lighting and appliances. The utility company will only supply a 6 AWG overhead triplex...

Sizing Wire [ 3 Answers ]

Im running a new 100amp sub about 40 ft from house. Ive been reading but wanted to know you guys' opinion. Should I go with THWN #3 for my Hots/Neutrals. And #8 for EQ Gnd.? I'm kind of confused about the 90/75 degrees that rate this type wire. Also I understand about having to conduit...

Wire Size for 150 amp service 300 feet [ 1 Answers ]

I need to take electrical service 300 feet to my barn. I want to take a 150 amp service. What wiresize to I use for this effort.

Electrical Service Sizing [ 5 Answers ]

I have 2 electrical subpanels to install off my home's service. My home service is 800 Amps. These will be taken as 2 separate runs off my main service box. The first is for a barn which is 250 feet away and I want to put in a 100 Amp panel. The second will run to a well house which is 300...


View more questions Search