    Electrical Service Sizing
    I have 2 electrical subpanels to install off my home's service. My home service is 800 Amps. These will be taken as 2 separate runs off my main service box.

    The first is for a barn which is 250 feet away and I want to put in a 100 Amp panel.

    The second will run to a well house which is 300 feet away. This will power a few things. One is a shallow well pump located in the well house. I want to come off this panel to run 7 post lights along my driveway (Each light has a 150 Watt bulb. 1 light will be at the well house. 2 lights will be spaced 100 feet apart towards my home and the other 4 lights will be spaced 100 feet apart away from the well house in the opposite direction. I also want to have an outdoor receptacle at each post for Christmas decorations. Also, there will be 2 gate motors at the far end of the lights around 350 feet away from the well house (motors are stepped down to 24 V dc.) I am unsure what amperage to place here.

    The obvious questions are what size wiring and what size conduit? Anything not obvious I need to look out for? I am confident I can handle the wiring of the panels, etc but the sizes of the runs bother me.

    Any help is appreciated.

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 17, 2006, 04:42 PM
    I would use #4/0 URD four wire cable to feed the panel.

    Use #2 URD four wire cable to each light post, and to the motors.

    If the path is rocky or difficult to lay cable in a bed of sand 6 " below and above, then use 4" DB PVC duct in a two foot to the top of the conduit,trench. If the soil is very rocky, lay a bed of sand above and below the conduit.

    If the conduit crosses under a road or drive with heavy truck traffic, trench should be 36" deep.

    Lay warning tape the entire length 12" below grade over the conduit.

    At each post use a small handhole, 12" x 18" to junction to a smaller #10-3 with ground UF cable to each post. Use 1" conduit into each post. Can you splice in the pole base?

    Use a in ground handhole at the panel also to change over to a smaller 2" conduit into the panels.

    Be sure to treat the AL cable connections with aluminum rated connectors, anti oxidant compound, and torque the connections.

    Hope this helps.
    bhayne's Avatar
    bhayne Posts: 339, Reputation: 4
    Full Member
     
    #3

    Oct 18, 2006, 03:05 PM
    Accurate calculation depends if you have 3 phase service at 208V or single phase at 240/ 120V.

    3 phase transmits approximately 3X the power but the conductors will have a greater voltage drop and will be sized larger. Best to know now because if you undersize your supply conductors it will get expensive.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 18, 2006, 03:35 PM
    I believe most utilities do not allow single family residential buildings, and most rural areas to use three phase, but certainly something to be sure of.

    208 volts will skew the calculations.

    But speaking of accurate calculations:

    100 Amps at 240 volts single phase = 24000 watts of power

    100 Amps at 208 volts three phase = 35984 watts of power

    Or doubled the amount of power, at voltage reduced by 13%
    mkgal4's Avatar
    mkgal4 Posts: 2, Reputation: 1
    New Member
     
    #5

    Oct 18, 2006, 07:41 PM
    Quote Originally Posted by mkgal4
    I have 2 electical subpanels to install off of my home's service. My home sevice is 800 Amps. These will be taken as 2 seperate runs off of my main service box.

    The first is for a barn which is 250 feet away and I want to put in a 100 Amp panel.

    The second will run to a well house which is 300 feet away. This will power a few things. One is a shallow well pump located in the well house. I want to come off of this panel to run 7 post lights along my driveway (Each light has a 150 Watt bulb. 1 light will be at the well house. 2 lights will be spaced 100 feet apart towards my home and the other 4 lights will be spaced 100 feet apart away fom the well house in the opposite direction. I also want to have an outdoor receptacle at each post for Christmas decorations. Also, there will be 2 gate motors at the far end of the lights aound 350 feet away fom the well house (motors ae stepped down to 24 V dc.) I am unsure what amperage to place here.

    The obvious questions are what size wiring and what size conduit? Anything not obvious I need to look out for? I am confident I can handle the wiring of the panels, etc but the sizes of the runs bother me.

    Any help is appreciated.

    Thanks
    Thanks for the good info. I want to avoid aluminum if possible (even though copper is more $$) to avoid any connection trouble. I had some reliability issues with an older house that had some aluminum coming into copper. How would that affect the wire sizing?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Oct 18, 2006, 08:15 PM
    Then 2/0 in place of the 4/0 and still use #2 copper for the other.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bow Sizing [ 2 Answers ]

How does one determine what size bow to buy? I have noticed many lengths and draw distances. I don't want to spend a lot of money on a bow to find out it is not comfortable to use.

What type of electrical service do I need? [ 13 Answers ]

My name is JC and I was wondering what type of electrical service I need. My circuit breaker panel only has 26 breakers in it and it is 100 AMPS. The electrician says I will need increase my service to 200 AMPS. This will give me room for 40 Breakers. I am rewiring the house and I do not have...

Image sizing [ 7 Answers ]

I downloaded a thumbnail image, is it possible to enlarge it without blurring the image? It is in GIF format.

Conduit sizing? [ 4 Answers ]

Hi all! I am relocating my breaker box approx 30 feet from its original location. Installing splice box in the old location for connections. My question is : I have 14 12-2 and 3 12-3 to pull from new box to splice box what size conduit do I need so not to worry about heat build up or de-rating...

Sizing Furnace [ 2 Answers ]

I'm finishing my basement and I'm trying to identify if my existing furnace is large enough to heat the basement. Here are the details. I have a Trane XE 80 LP furnace with a 100,000 BTU input rating and it's an 80% furnace. My house is 2250 square feet EXCLUDING the basement. I'm finishing 700...


View more questions Search