    Wiring a Hot Tub
    I just got a old 2-3 person hot tub. The pump motor is a 16.4 amp11 volt and I believe the heater controller is as follows:

    Porter & Blumfield
    > KUP 14A15 - 120
    > 120V 50/60 Hz
    > Industrial Rated
    > 3A 1/hp 600 VAC

    > 10A 1/3 hp 120 VAC
    > 6 2/3A 1/3 HP 250 VAC
    > Appliance Rated
    > 10A 250 VA
    The previous owner did not have a GFCI breaker in the connection. He was using 10/3 with a ground wiring to a subpanel.

    What size and type of GFCI breaker do I need in the GFCI Breaker box. (ie 20 amp 2 pole, 20 amp tandem or a 20 amp 1 pole breaker)?

    What size of breaker should I use in the main panel?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jun 26, 2009, 06:42 AM

    It should have Supply connections, If 4 wire/240 volts, use a double pole 240 volt GFI breaker, Nameplate should say.
    SLIDER53's Avatar
    SLIDER53 Posts: 5, Reputation: 1
    New Member
     
    #3

    Jun 26, 2009, 10:30 AM
    The only thing on the Nameplate or label is "Poly-Recliner Spa Shell" 207270 Manufactured by Polynesian Pools & Spas Inc EXT 46 1982. There are no electrical plates in the control box under the spa.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jun 26, 2009, 12:35 PM
    I see you only provide partial info on the pump motor:

    The pump motor is a 16.4 amp11 volt

    Finish and provide the voltage rating of the pump.

    If you eant 120 volts, this motor alone will need a 30 amp breaker.

    Next you provide the heater controller info, but no details on the actual heater, such as wattage or voltage.

    Knowing only the controller ratings is irrelevant.

    Can you find more detail on the heater itself?

    You may start with a 30 amp 120/240 volt circuit with a 30 amp 2 pole breaker and #10 wire, but then what if the unit needs more? You will then need to install all #8 wire and a 2 pole 40 amp breaker, or whatever will be needed.

    I realize this is why your asking, so you do it right the first time. We just need more complete an accurate info to be able to help.
    SLIDER53's Avatar
    SLIDER53 Posts: 5, Reputation: 1
    New Member
     
    #5

    Jun 27, 2009, 08:37 AM
    Quote Originally Posted by tkrussell View Post
    I see you only provide partial info on the pump motor:

    The pump motor is a 16.4 amp11 volt

    Finish and provide the voltage rating of the pump.

    If you eant 120 volts, this motor alone will need a 30 amp breaker.

    Next you provide the heater controller info, but no details on the actual heater, such as wattage or voltage.

    Knowing only the controller ratings is irrelevant.

    can you find more detail on the heater itself?

    You may start out with a 30 amp 120/240 volt circuit with a 30 amp 2 pole breaker and #10 wire, but then what if the unit needs more? You will then need to install all #8 wire and a 2 pole 40 amp breaker, or whatever will be needed.

    I realize this is why your asking, so you do it right the first time. We just need more complete an accurate info to be able to help.
    The heater plate was on the back side of the heater control 5.5KW 240v
    The pump motor is 115 volts / 16.4 / 4.4 60 Hz,
    There is a 30 amp what appears to be a breaker in the wiring box
    I tried to send a picture but the file is too large for this site.
    Hope this will help Thanks for your help
    Attached Images
      
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jun 28, 2009, 04:47 AM
    The photos show contactors. I get that you think there is a 30 amp breaker but could not upload a photo of that.

    The 5.5 KW heater at 240 volts will draw 23 amps. The pump motor draws 16 amps at 120 volts.

    Is it possible that the tub had one 240 volt circuit for the heat and a 120 volt circuit for the pump? This is not typical.

    If both the heat and pump need one circuit, my calculations show that a 50 Amp 4 wire 120/240 volt feeder, with two hots, a neutral, and an equipment ground is needed. This can be either #6-3 Romex or #8-3 MC cable.

    Do your best to upload a picture of the device you think is a breaker, and perhaps a wiring diagram.

    If both heat and pump use one circuit, I do not see how it worked with a 30 amp circuit.
    SLIDER53's Avatar
    SLIDER53 Posts: 5, Reputation: 1
    New Member
     
    #7

    Jun 28, 2009, 07:17 PM
    Quote Originally Posted by tkrussell View Post
    The photos show contactors. I get that you think there is a 30 amp breaker but could not upload a photo of that.

    The 5.5 KW heater at 240 volts will draw 23 amps. The pump motor draws 16 amps at 120 volts.

    Is it possible that the tub had one 240 volt circuit for the heat and a 120 volt circuit for the pump? This is not typical.

    If both the heat and pump need one circuit, my calculations show that a 50 Amp 4 wire 120/240 volt feeder, with two hots, a neutral, and an equipment ground is needed. This can be either #6-3 Romex or #8-3 MC cable.

    Do your best to upload a picture of the device you think is a breaker, and perhaps a wiring diagram.

    If both heat and pump use one circuit, I do not see how it worked with a 30 amp circuit.
    The photos were 2 shots of what I thought was a 30 amp breaker. I am trying to locate a manual for the spa but it is over 20 years old an the company is no longer in busincess.
    Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring direction for a multi wiring system thermostat! [ 3 Answers ]

I have a 2 wire system (3 phase), need to connect multi wiring system thermostat! Need to know if, its correct to just use line#1, and the device already has a jumper?

Janitrol wiring to rth3100c wiring [ 1 Answers ]

I've taken off the cover and the wires are all OK but the black one where does it go to? My heater won't come on (well some times the AC come on with out me turning it on.)

Honeywell wiring different from old thermostat wiring [ 2 Answers ]

I purchased a non-programmable digital thermostat to replace an analog thermostat with wiring red, white yellow and black. How do I match the wiring? HELP!!

John Deere - My dog ripped the wiring Out - Need Wiring Diagram or photos [ 2 Answers ]

I have a 3 year old L110 that ran fine until last week. I think my dog chased a chipmunk up under the hood and in trying to get to him ripped a bunch of wires out. I have spliced back together the obvious wires (color coded) but I have one black wire that I assume is a ground(?) and the two...


View more questions Search