Originally Posted by
tkrussell
I see you only provide partial info on the pump motor:
The pump motor is a 16.4 amp11 volt
Finish and provide the voltage rating of the pump.
If you eant 120 volts, this motor alone will need a 30 amp breaker.
Next you provide the heater controller info, but no details on the actual heater, such as wattage or voltage.
Knowing only the controller ratings is irrelevant.
can you find more detail on the heater itself?
You may start out with a 30 amp 120/240 volt circuit with a 30 amp 2 pole breaker and #10 wire, but then what if the unit needs more? You will then need to install all #8 wire and a 2 pole 40 amp breaker, or whatever will be needed.
I realize this is why your asking, so you do it right the first time. We just need more complete an accurate info to be able to help.