    No power going to AC unit
    Hello I have problem with my AC there in no power going out to the unite I have check all the fusses I could find the one outsider by the unit it was fine put there was no power I used my voltmeter also I blower working good the thermostats also working fine it turn on and off and if you change the setting the blower will response to it I check the conction on the fan timer controller board I didn't see any thing wrong dose any one have any idea what is wrong
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Jun 21, 2009, 08:31 AM

    You have now 220 volts? Or 24 volts? Does the unit run if you push in the contactor?
    elsohage's Avatar
    elsohage Posts: 6, Reputation: 1
    New Member
     
    #3

    Jun 22, 2009, 08:42 AM
    Quote Originally Posted by Joshdta View Post
    You have now 220 volts? or 24 volts? Does the unit run if you push in the contactor?
    Yes the unit will run when I puch on the contactor. Do you think the problem with the contactor and if so could be fix or I have to buy know one I do have good knowledge
    Thank you
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #4

    Jun 22, 2009, 11:37 AM
    Is probably low voltage prob. Check the smaller tstat wire going to the contactor,for 24 volts.trace the wire back to the furnace if you don`t have 24 volts, looking for chewed or broken wires. Have you checked the circuit board for a blown automotive type push-in fuse
    Let us know what you find
    elsohage's Avatar
    elsohage Posts: 6, Reputation: 1
    New Member
     
    #5

    Jun 24, 2009, 07:20 AM
    Quote Originally Posted by wmproop View Post
    is probably low voltage prob. check the smaller tstat wire going to the contactor,for 24 volts.trace the wire back to the furnace if you don`t have 24 volts,,lookin for chewed or broken wires. have you checked the circuit board for a blown automotive type push-in fuse
    let us know what you find
    It is me again I have change the contractor and it work . I solve the first problem now I have anther problem the fan work fine and it response to the thermostat but the problem now with the compressor it won't kick in it did the first time I pushed on the bad contactor before I change it when I put the new one in it didn't work I changed the capacitor too and yet no compressor I check all the wiring it is fine the power going in to the compressor is 230V but the one going to the fan is 330 that reading from the capacitor to the fan but from the contactor it is 226V in and out so what you think the problem there a button in the side said reset I did push this one also and there was no different
    elsohage's Avatar
    elsohage Posts: 6, Reputation: 1
    New Member
     
    #6

    Jun 24, 2009, 05:28 PM

    I have change the contractor and it work . I solve the first problem now I have anther problem the fan work fine and it response to the thermostat but the problem now with the compressor it won't kick in it did the first time I pushed on the bad contactor before I change it when I put the new one in it didn't work I changed the capacitor too and yet no compressor I check all the wiring it is fine the power going in to the compressor is 230V but the one going to the fan is 330 that reading from the capacitor to the fan but from the contactor it is 226V in and out so what you think the problem there a button in the side said reset I did push this one also and there was no different
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #7

    Jun 24, 2009, 06:01 PM

    Sounds to me like you have got a wire put in the wrong place either on the contactor or the capacitor.
    elsohage's Avatar
    elsohage Posts: 6, Reputation: 1
    New Member
     
    #8

    Jun 24, 2009, 09:56 PM
    Quote Originally Posted by Joshdta View Post
    sounds to me like you have got a wire put in the wrong place either on the contactor or the capacitor.
    I did a Diagram before I take them off but if I did any mistake will be in the contactor
    elsohage's Avatar
    elsohage Posts: 6, Reputation: 1
    New Member
     
    #9

    Jun 26, 2009, 06:14 AM

    Thank you guys it fix now
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #10

    Jun 26, 2009, 12:29 PM

    What did you find the problem was?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How much power will my new A/C unit really consume? [ 6 Answers ]

Hello, We just got a new a/c unit (outside condenser) with the following specs. Cooling Capacity : 30000btu 208/60 Min. circuit amp: 16.2 Compressor: Rated Load Amps: 11.8 Locked Running Amps: 73

HVAC unit power [ 1 Answers ]

How do I turn off the HVAC unit power?

New ac unit no power [ 4 Answers ]

Help! I have a brand new air conditioner and furnace and I cannot get the a/c on. I have read many sites and the problem seems to be no power to the outside unit. I have checked the breakers, but assume it hasn't been tripped as it has never been on! The other problem is that my panel is not...

Difference between a Power Distribution Unit (PDU) and a Remote Power Panel (RPP) [ 1 Answers ]

Is there any difference between a Power Distribution Unit (PDU) and a Remote Power Panel (RPP) in context of data center? If yes, then what is it?. Thanks.

No power in therm unit [ 8 Answers ]

Hi, I need help fixing ac unit. I called the help desk for my Hunter thermostat and they had me try and start the fan using a metal paper clip. The problem before I did that was that it wasn't starting. There was power but it wasn't regulating the temp. Well in the process I cause a shortage...


View more questions Search