New Member
|
|
Jun 20, 2009, 09:52 PM
|
|
No power going to AC unit
Hello I have problem with my AC there in no power going out to the unite I have check all the fusses I could find the one outsider by the unit it was fine put there was no power I used my voltmeter also I blower working good the thermostats also working fine it turn on and off and if you change the setting the blower will response to it I check the conction on the fan timer controller board I didn't see any thing wrong dose any one have any idea what is wrong
|
|
 |
Ultra Member
|
|
Jun 21, 2009, 08:31 AM
|
|
You have now 220 volts? Or 24 volts? Does the unit run if you push in the contactor?
|
|
 |
New Member
|
|
Jun 22, 2009, 08:42 AM
|
|
 Originally Posted by Joshdta
You have now 220 volts? or 24 volts? Does the unit run if you push in the contactor?
Yes the unit will run when I puch on the contactor. Do you think the problem with the contactor and if so could be fix or I have to buy know one I do have good knowledge
Thank you
|
|
 |
Ultra Member
|
|
Jun 22, 2009, 11:37 AM
|
|
Is probably low voltage prob. Check the smaller tstat wire going to the contactor,for 24 volts.trace the wire back to the furnace if you don`t have 24 volts, looking for chewed or broken wires. Have you checked the circuit board for a blown automotive type push-in fuse
Let us know what you find
|
|
 |
New Member
|
|
Jun 24, 2009, 07:20 AM
|
|
 Originally Posted by wmproop
is probably low voltage prob. check the smaller tstat wire going to the contactor,for 24 volts.trace the wire back to the furnace if you don`t have 24 volts,,lookin for chewed or broken wires. have you checked the circuit board for a blown automotive type push-in fuse
let us know what you find
It is me again I have change the contractor and it work . I solve the first problem now I have anther problem the fan work fine and it response to the thermostat but the problem now with the compressor it won't kick in it did the first time I pushed on the bad contactor before I change it when I put the new one in it didn't work I changed the capacitor too and yet no compressor I check all the wiring it is fine the power going in to the compressor is 230V but the one going to the fan is 330 that reading from the capacitor to the fan but from the contactor it is 226V in and out so what you think the problem there a button in the side said reset I did push this one also and there was no different
|
|
 |
New Member
|
|
Jun 24, 2009, 05:28 PM
|
|
I have change the contractor and it work . I solve the first problem now I have anther problem the fan work fine and it response to the thermostat but the problem now with the compressor it won't kick in it did the first time I pushed on the bad contactor before I change it when I put the new one in it didn't work I changed the capacitor too and yet no compressor I check all the wiring it is fine the power going in to the compressor is 230V but the one going to the fan is 330 that reading from the capacitor to the fan but from the contactor it is 226V in and out so what you think the problem there a button in the side said reset I did push this one also and there was no different
|
|
 |
Ultra Member
|
|
Jun 24, 2009, 06:01 PM
|
|
Sounds to me like you have got a wire put in the wrong place either on the contactor or the capacitor.
|
|
 |
New Member
|
|
Jun 24, 2009, 09:56 PM
|
|
 Originally Posted by Joshdta
sounds to me like you have got a wire put in the wrong place either on the contactor or the capacitor.
I did a Diagram before I take them off but if I did any mistake will be in the contactor
|
|
 |
New Member
|
|
Jun 26, 2009, 06:14 AM
|
|
Thank you guys it fix now
|
|
 |
Ultra Member
|
|
Jun 26, 2009, 12:29 PM
|
|
What did you find the problem was?
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
How much power will my new A/C unit really consume?
[ 6 Answers ]
Hello,
We just got a new a/c unit (outside condenser) with the following specs.
Cooling Capacity : 30000btu
208/60
Min. circuit amp: 16.2
Compressor:
Rated Load Amps: 11.8
Locked Running Amps: 73
New ac unit no power
[ 4 Answers ]
Help! I have a brand new air conditioner and furnace and I cannot get the a/c on. I have read many sites and the problem seems to be no power to the outside unit. I have checked the breakers, but assume it hasn't been tripped as it has never been on! The other problem is that my panel is not...
No power in therm unit
[ 8 Answers ]
Hi, I need help fixing ac unit. I called the help desk for my Hunter thermostat and they had me try and start the fan using a metal paper clip. The problem before I did that was that it wasn't starting. There was power but it wasn't regulating the temp. Well in the process I cause a shortage...
View more questions
Search
|