    #1

    Mar 25, 2009, 05:50 PM
    Wiring Shed for 20A Using 12/2 and 115 Recepticles
    A novice here...

    Have a shed with current 115v service. I want to go to 220 using 12/2. My understanding is, black and white wires go together and then you have the (bare) ground.

    My current recepticles are 115 ( I think) two poles on each side. I believe the ground is pigtailed.

    My questions, given I only have two wires to connect..

    1) How do I pass through the recepticles with service?

    2) I need to put a GFIC on the front of the leg... how do I wire for that?

    I've got a Cutler-Hammer BR220 120/240 2 pole breaker.

    Thanks Very Much Barry
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Mar 25, 2009, 06:15 PM

    You can change the breaker and shed to 240 volts, problem is you woun't have any 120 volts as you have no neutral.
    If you need both, you will need to upgrade wiring, more, and or bigger.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Mar 25, 2009, 06:34 PM
    Barry, why do you want to "go to 220"??
    Are you adding a new 240v circuit and leaving the existing 120v circuit?
    What is this new 240v circuit for?

    You CANNOT have both 240v and 120v using only a 12/2 cable. That 12/2 can be either 120v or 240v. NOT both.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Mar 25, 2009, 06:36 PM
    Re-reading I see what you want to do. You cannot with the 12/2. You need 12/3 in order to do what you want.
    barryb38583's Avatar
    barryb38583 Posts: 2, Reputation: 1
    New Member
     
    #5

    Mar 25, 2009, 06:46 PM
    Sorry guys, I meant, go to 20a service using my existing 15a 12/2 wiring.

    Quote Originally Posted by barryb38583 View Post
    A novice here......

    Have a shed with current 115v service. I want to go to 20amps using 12/2. My understanding is, black and white wires go together and then you have the (bare) ground.

    My current recepticles are 115 ( I think) two poles on each side. I believe the ground is pigtailed.

    My questions, given I only have two wires to connect..

    1) How do I pass through the recepticles with service?

    2) I need to put a GFIC on the front of the leg...how do I wire for that?

    I've got a Cutler-Hammer BR220 120/240 2 pole breaker.

    Thanx Very Much Barry
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Mar 26, 2009, 08:37 AM
    New to this thread. Assumption: This is a Remote shed, it is not attached to the residence.

    Let's get some real basic information for the original poster.

    Most household cabling is listed for 600 VAC or less.

    Electricity is distributed to the residence through a Lateral (below ground) or service drop (above Ground)

    The power company provides 240 VAC to the residence via 2 ungrounded (hot) conductors and 1 grounded (Neutral) conductor.

    These conductors in turn feed the two hot phases of the main panel and the one Neutral connection. The Neutral conductor is "Bonded" (electrically joined) together, then the panel is grounded via an equipment grounding conductor to either grounding rods or the cold water pipe.

    Most homes would use a 14/2 cable to feed a standard 15 amp receptacle. Black is connected to the darker screw and white is connected to the silver screw terminal.

    Now given all of above, let's explore what you may be trying to do in your shed.

    To bring 240 VAC to the shed, you need to use two tandem breakers inside the main panel box. Each 20 amp Breaker and using the same handle. You must use a 12/3 with ground cable to carry the power to the shed.

    At the shed, you must attach each hot conductor (Black and Red) to a Phase Lug connector. The White (Grounded Conductor or Neutral) connects to the Neutral bus. It must be isolated from the subpanel grounding system.

    Now you can start to fan out your shed's wiring to at least one light. The receptacles must be GFCI protected.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #7

    Apr 13, 2009, 03:10 AM
    Have a shed with current 115v service. I want to go to 20amps using 12/2. My understanding is, black and white wires go together and then you have the (bare) ground.

    My current recepticles are 115 ( I think) two poles on each side. I believe the ground is pigtailed.

    My questions, given I only have two wires to connect..

    1) How do I pass through the recepticles with service?

    2) I need to put a GFIC on the front of the leg...how do I wire for that?

    I've got a Cutler-Hammer BR220 120/240 2 pole breaker.

    Thanx Very Much Barry


    Still doesn't make sense. You have a 120 volt branch circuit going to the shed, wired in 12/2 wire. (I'm assuming a buried UF cable, 12-2G)

    If you simply want 20 amps at 120 volts, no. 12 AWG is rated for 20 amps. The only reason someone would run No. 12 for 15 amps is either for voltage drop if it is a long distance, or if they happened to have some laying around and decided to use it.

    But... you have a 2-pole breaker, which means you are considering 240 volts. You have existing 120 volt receptacles you want to keep, so you need a neutral. This means you have more than one branch circuit, so you need a sub-panel in the shed.

    You can't do this with 12-2 cable. You need 4 wires to be code compliant. (Two hots, a neutral, and a ground)

    As far as putting a GFCI in the circuit. Determine which is the first receptacle in line. Wire the "home run" into the LINE side terminals on the GFCI. Connect the wires leading to the other receptacles into the Load terminals.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring the Potting Shed [ 3 Answers ]

I have a potting shed about 60 feet from my back door. I want to wire it and then post 2 to 4 electrical outlets for outdoor use on my privacy fence near the shed. (within 50 feet on either side of the shed). Any ideas on how to do this without spending a million dollars? Thanks.

Wall recepticles not working [ 6 Answers ]

This morning one wall of recepticles stopped working. The fridge is on one of them and was on earlier then suddenly stopped. I checked the two GFI's that run in the kitchen (one under the sink and one on the breaker box). How can I figure out what happened? I am not even sure if I know which...

Shed Wiring Question [ 1 Answers ]

Hello, I know this subject has probably been beaten into the ground but I have a question about wiring my 10 x 10 shed. All I want is a couple of outlets and two lights, one outside and one inside. The outlets will be for occasional power tool use, nothing heavy duty. I want to run a double 20 Amp...

Wiring a shed [ 2 Answers ]

I just finished building a storage shed and want some electricity out there... what type of wiring and cost would it be to run 30-40 feet or wire?what other materials am I going to need? Thanks for any suggestions... later

Shed/Barn wiring [ 2 Answers ]

I've got a decent sized shed out about 150ft from the house, I plan on running the cable underground in conduit. But I am unsure of what style/size cable I need to use for a 50A circuit 220/240V. I'm assuming that I probably need to use service entrance cable and can't use 6G stranded. I've tried...


View more questions Search