    Shed Wiring Question
    Hello,
    I know this subject has probably been beaten into the ground but I have a question about wiring my 10 x 10 shed. All I want is a couple of outlets and two lights, one outside and one inside. The outlets will be for occasional power tool use, nothing heavy duty. I want to run a double 20 Amp circuit from my outside panel using 12-3 w/ground uf (one neutral, two hots, one ground) from a 20 220v GFCI breaker and use a 20 amp dp switch as a disconnect at the shed. I will then split it off into 2 different 20 amp circuits, one for the outlets and one for the lights. I want to know if you think an 80 foot run of wire is too far for 12 gauge wire and are there any grounding issues with this type of disconnect setup?I have thought about the subpanel route but the electricity use in this shed will be minimal, mainly during the landscape season. Any response is greatly appreciated.
    Thanks,
    Jaime
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 26, 2007, 03:45 PM
    If the #12 wire has a load of 16 amps, the voltage drop will exceed the recommended 3% a bit. I realize it would cost more, but I would suggest using #10 wire. This will help with motor loads, and allow a bit more usage in the future.

    If the load is as minimal as you think then #12 is fine, just remember that later on if any more load is added, you may wish you had #10. Just a thought, it is entirely up to you. Consider if you use a long extension cord from the shed outlet, the voltage drop will show up then even with a minimal load.

    The grounding and the use of a 2 pole GFI CB sounds fine, just be sure to use the breaker that is rated 120/240 volt, this will have the neutral lug and pigtail.

    The 2 pole switch/disconnect is not necessary, but OK to have if you desire.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a shed [ 2 Answers ]

I just finished building a storage shed and want some electricity out there... what type of wiring and cost would it be to run 30-40 feet or wire?what other materials am I going to need? Thanks for any suggestions... later

Shed/Barn wiring [ 2 Answers ]

I've got a decent sized shed out about 150ft from the house, I plan on running the cable underground in conduit. But I am unsure of what style/size cable I need to use for a 50A circuit 220/240V. I'm assuming that I probably need to use service entrance cable and can't use 6G stranded. I've tried...

Wiring question [ 1 Answers ]

I'm installing a 240 volt electric baseboard heating system that has a total watts of 5,000. A 2500 and a 1500 watt unit will each have their own wall thermostat. Then there will be two 500 watt units each with their own unit mounted thermostat. I plan on using a 30 amp breaker and 10-2 wire. ...

Wiring question [ 2 Answers ]

Ok, I"ll try to explain this with the best of my ability. I have recently been trying to replace some of the light fixtures in my house. I have only lived in my house 3 months so I am not sure what I have yet. I only know it is 67 years old. What I noticed is there isn't black and white wires but...

Question about wiring [ 5 Answers ]

A neighbor of mine commented that the fan for his AC/heater unit is wired in a somewhat unorthodox (or is it?) fashion. On the 220 line, he has 2 parallel 40 amp breakers feeding 2 sets of wires whose load is the fan. Essentially, it looks like the electricians that did the work (before he owned...


View more questions Search