    Adequate wire size for 5- fixture circuit ?
    I'm on the home stretch in a garage to apt remodel. One remaining task is to put 5 , single lamp fixtures on the exterior wall. The power is a 12/2 nm, 20 amp breaker circuit from panel to switch, roughed in the wall to the center fixture box location. This will also be the j-box for the remaining fixtures. I am going to have to do some fishing and finessing to get the wire from the j-box to the fixtures. Each fixture will have a single 60 watt lamp. My questions: Would it be easier to pull 14-2 nm to the other fixtures? Can I use 14- 2 ? Is it worth getting a 25' roll of 14-2 or should I just stick to 12-2nm? Every other circuit has been pulled in 12-2 or 12-3
    Thanks, packrat
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Apr 6, 2009, 10:56 AM
    Do not change wire sizes. By doing so you are only wasting the larger wire since you MUST use the breaker appropriate for the smallest wire on the circuit.

    Either use all #14 or all #12. If you used #12 everywhere else it makes no sense to change it now.
    561packrat's Avatar
    561packrat Posts: 80, Reputation: 1
    Junior Member
     
    #3

    Apr 6, 2009, 11:06 AM
    Quote Originally Posted by stanfortyman View Post
    Do not change wire sizes. By doing so you are only wasting the larger wire since you MUST use the breaker appropriate for the smallest wire on the circuit.

    Either use all #14 or all #12. If you used #12 everywhere else it makes no sense to change it now.
    Makes sense, will comply
    Thanks for the advice stanfortyman.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Wire size for 100 amp 3 phase circuit [ 1 Answers ]

I am installing a commercial convection oven rated as follows: 220V 3 Phase. The oven pulls 23 kilowatts. I calculate this to be about 64 maximum amps. So, I'll use a dual pole GE 100 amp breaker in my box. The wire run will be about 15 feet through conduit. I'm getting conflicting reports on...

Adequate conduit size for range and water heater wire [ 1 Answers ]

I want to place pvc conduit in walls that I am going to close up with drywall. The jobsite is a detached garage, into an apt. previously unfinished. I would like to have the conduit in wall so when I get to the point where I can afford the appliances and conductor I can move forward. There will be...

What size fixture? [ 2 Answers ]

What size drain fixture should I buy for a 1.75 inch drain hole? I have a vessel sink with a 1.75 in hole, but I have not seen a push button drain in that size. Should the drain be smaller than the hole, such as 1.5 or 1.25? This link goes to the kind of thin I am looking for Porcelain Vessel...

Adequate conductor size for art studio/ apt. [ 6 Answers ]

Converting detached garage to art studio/ apt. What is recommended conductor size to bring service from separate meter based on following:(1) approx. 70' including vert. run in 2' pvc, buried 2' to top. (2) anticipate 150 amp panel (3) My wife wants;tankless water heater, stove/oven,...


View more questions Search