    Sub Panel Wire
    I recently did a walkthrough with the electrician who is helping me get my basement wired up. During that time I believe he had told me to pick up approximately 10ft of 4/4/2 electrical wire to run a 100A Breaker from my 200A panel to a 100A sub panel. Another guy told me I should get 4/3 wire because there shouldn't be a need for a ground on the sub panel as it would just create a loop. Both guys are great with electrical and from my understanding, know their stuff.

    What wire size will I need to run from my 200A main breaker to the 100A sub panel?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Mar 30, 2009, 05:46 PM
    Create a loop??

    The guy who told you to get a wire without a ground does NOT know his stuff.

    I assume because of the short 10' distance this is within the same structure as the main panel.

    Previously any sub panel within the same structure as the main panel required a "4-wire" feeder. Two hots, neural and a ground. Detached structure sub-panels had exceptions to this rule.
    In the 2008 NEC ALL sub-panels require a 4-wire feeder.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Mar 30, 2009, 06:27 PM

    Ground is usually assumed in electrical work.
    Just as 14/2 is 2 conductors is #14 with ground an this usually NM-B cable which implies the ground.

    Thus in your notation, the cable type is not specified. We can assume that it's NM-B.

    Thus 4-4-2 allows a higher neutral current than 4/3. 4/3 is really 4-4-4 in the original notation. There is never any 2 conductor cable with two different wire sizes.

    4-4-2 is better than 4-4-4 and both likely contain a ground.

    I get 1-1-1 with a minimum of #6 ground

    Subpanels need the ground. Ground an neutral must not be connected in the sub-panel. Additional hardware may be required as well as removing a ground bond screw and purchasing an additional ground bar commonly called a "ground bar kit".

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting neutral wire to ground wire in breaker panel [ 3 Answers ]

Can the neutral wire be connected to the ground wire at the neutral bar in the breaker panel?

Connecting 3 wire to a 4 wire service panel [ 5 Answers ]

I am trying to connect from a 3 wire system at the utility pole to a 4 wire service panel inside a new mobile home. I called an electrician for some advice and was told that I needed to drive an 8ft ground stake and attach a solid copper wire from the stake to the ground bar in the panel. Then I...

3 wire to 4 wire from sub panel to receptacle [ 1 Answers ]

I am installing a new stove and running new romex from the box to the stove. How do I properly connect the 4 wires at the box that currently has only 3 wires so that the new system is grounded? Saw this above and it is similar to my question earlier, with the response being "yes" as to the box...

Wire for sub-panel [ 5 Answers ]

I want to install a sub panel in my shed The wire will probably run around 150' And I will have heating and air unit in the wall that needs a 230v line Plus 6 receptacles that were already installed there on a single line So I'm wondering what kind of a cable do I run to the sub panel?

Sub panel wire [ 2 Answers ]

I'm currently building a new home with 200amp service. I have requested the builder to supply 100 amp service to the rear of the home for my detached workshop. My question is a alumaflex type se cable 600 volt awg2-1 cdr awg4 the right cable? I have been told this is only rated at 65 amps? Thanks


View more questions Search