    How to get 120v from 208v
    I have 208v 3 phase in my building and to my machine, but I need 120v to run my conveyor. How can I wire it to get 120v off the 208 3 phase wires?
    I used the green, white and black wires and checking from the ground to each leg I get 125v but from leg to leg I get 211v. Can someone please help me?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Mar 19, 2009, 08:09 AM

    Well, you should have blue, black, red, white and green or taped as such. Your missing the white wire. A neutral has to be pulled from the 3 phase panel or the load should come from a single phase panel.

    3 phase motors don't need the neutral to function or be wired properly. You just need the three phases and protective ground. Depending on the equipment, neutral may be run.

    What you measured is correct.

    Sometimes it's advantageous to use a 120 V control voltage or even a 208 control voltage, it just depends on the equipment.

    The conveyor should have been purchased or wired for 208 with controls being at a lower voltage derived from a small control transformer.

    It's impossible to consider all of the possibilities without knowing more. I would suggest hiring an electrician.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Mar 19, 2009, 01:44 PM
    Quote Originally Posted by crites7 View Post
    how to get 120v from 208v
    You don't without a neutral.

    This is NOT a DIY job. Working in a commercial setting on three phase should ONLY be done by a qualified electrician.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

208V VS. 240V power [ 4 Answers ]

Hello, Just want a clarification: 208v power comes from a wye connection(ie two line wires) does 240 come from a delta connection? Please explain Regards, l. fudge

Convert 208v to 480v [ 2 Answers ]

We bought a 20kW UPS that is designed for 480V 3 phase. We are moving to a building that is only wired for 208V. Is there any way to convert 208 3phase to 480 volt 3 phase or will we need to scrap the UPS?

Convert 480V/3Ph to 208V/1P [ 1 Answers ]

I need 80 dedicated 208V/15 amp circuits. How many amps of 480V/3Ph service are required? Thanks for the help.

208v 3-Phase [ 1 Answers ]

Hello, We have a 208v 3-phase panel in our server room filled with 20amp circuits. We would like to change them to 30amp circuit that goes to the twist lock circuits so we can plug in bigger equipment. If all possible. What I can’t figure out is how many 30-amp circuits we can get in the 208v...

120v/208v single phase appliance wiring [ 2 Answers ]

Recently purchased a coffee machine that has the above reqts. I understand that it has 220 and 110v circuits that need power. I also purchased a generator to power this brewer outside. If I use a NEMA L14-30P plug, to connect into the generator, What is the sequence of wiring for the plug three...


View more questions Search