    Convert 480V/3Ph to 208V/1P
    I need 80 dedicated 208V/15 amp circuits. How many amps of 480V/3Ph service are required?

    Thanks for the help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 19, 2007, 09:24 AM
    I will assume this is commercial application, where the load will likely run 3 hours or more. Each circuit needs to be derated by 80%, so the total max load will be 12 amps per circuit.

    To answer your specific question, the amp load at 480 V 3 Ph will be 416 amps.

    You will need a transformer to handle at least 345.6 KVA of load plus 25%, or 432 KVA. The 480 volt feeder to the xfer also needs to be increased by 125% of the max load.

    The next standard size transformer is a 500 KVA. This is a very large transformer, about 6 feet wide, 6 feet high, and 5 feet deep, and there are certain requirements for installing this size transformer not to mention the weight to deal with.

    If this is for an IT equipment, use a K rated transformer.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

3ph motor [ 2 Answers ]

I have 15hp 3phase motor rated 460/230V how can I run my motor if my supply voltage is 380v 3phase...

208v 3-Phase [ 1 Answers ]

Hello, We have a 208v 3-phase panel in our server room filled with 20amp circuits. We would like to change them to 30amp circuit that goes to the twist lock circuits so we can plug in bigger equipment. If all possible. What I can’t figure out is how many 30-amp circuits we can get in the 208v...

Sizing Disconnects for 480v Temporary Service [ 3 Answers ]

How do I pick the right disconnect for 480v temporary service at a construction jobsite?

3ph motor [ 5 Answers ]

I'm having only a single phase supply. How can I run my 3phase motor without using A phase converter?

480v Stepped Down To 120/208v [ 10 Answers ]

If I have a 600A 480v service and I step in down to 120/208, will I have an increase of available amperes at the lower voltage? Or will the amperage remain the same no matter how I change the voltage? Thanks


View more questions Search