    newanimal7's Avatar
    newanimal7 Posts: 4, Reputation: 1
    New Member
     
    #1

    Mar 19, 2009, 08:10 AM
    Sharing common groung wire OK?
    I'm running 240v to 100 amp subpanel about 90 ft via pvc conduit. Also two 20 amp branches about midway to ext. outlets via same conduit. Can I ground those outlets tying to same ground wire (10 gauge) running to sub? If so, should I increase gauge size from that point to main? Thanks!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 19, 2009, 08:36 AM
    First off, a 100 amp feeder must use a minimum of a #8 equipment grounding conductor, not #10, per Table 250.122 of the NEC.

    See a sticky at the beginning of this forum to gain access to read the NEC.

    Once the proper size EGC is installed for the 100 amp feeder, it can be used to ground the receptacles that are midway in the conduit run.

    I am assuming there are #12 branch circuit wires in the conduit to feed these outlets, along with the 100 Amp feeder conductors?
    newanimal7's Avatar
    newanimal7 Posts: 4, Reputation: 1
    New Member
     
    #3

    Mar 19, 2009, 10:04 AM

    Thanks tk. I haven't done anything yet. Yes, I'll be using #12 for the 20amp branches. I am to find the desired info from the nfpa/nec code guide as yet. A union electrician neighbor what gauges would "be fine". Hence the #10 for the ground. I suppose the #8 for the hot feeds to the sub he suggested should rather be #6 as well right?
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #4

    Mar 19, 2009, 11:21 AM

    I don't think your neighbor understood that this is to be a 100 amp sub panel.

    You need #4 copper or #2 aluminum for the hots and neutral and #8 copper or #6 aluminum for grounding.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Mar 19, 2009, 03:01 PM
    Ummm...


    Quote Originally Posted by newanimal7 View Post
    I am to find the desired info from the nfpa/nec code guide as yet.
    What?

    If this guy:

    Quote Originally Posted by newanimal7 View Post
    A union electrician neighbor what gauges would "be fine". Hence the #10 for the ground.
    Did know this was to be a 100Amp panel/feeder, run don't walk from any advice he gives.

    Is someone guessing here:

    Quote Originally Posted by newanimal7 View Post
    I suppose the #8 for the hot feeds to the sub he suggested should rather be #6 as well right?
    Good thing nothing was done yet. Best you explain the entire plan with sizes of everything, and there are several experts here that will explain in detail what works and does not, starting with Tev, he sized your feeder conductors for you. There are many other details that are needed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is the common wire? [ 20 Answers ]

I'm changing my old thermostat by one programmable; the new thermostat don't use batteriesand the wires that I have available are Y, G, R, W, what wire can I use in the x or common wire?

Common wire in furnace [ 1 Answers ]

I had a furnace "expert" come in because I kept blowing a fuse in the furnace. He by passed a common wire. The furnace is an American Standard and it is brand new. It is an electric furnace. I only run it about 3 to 4 hours per day. I received my first power bill it was extremely high. I was...

Common Outlets for 10/2 wire [ 10 Answers ]

Are there any outlets that take a common household plug which are designed for 10/2 wire and 110V? I've found some outlets that are good for 20A, but not 30A. Would the 20A receptacles work with 10/2 wire?

Common Thermostat Wire [ 1 Answers ]

I am trying to install a new thermostat which requires a common wire for use. I however only have a Y,O,R, and G currently. There is a blue wire in the bundle that was installed however at the 24V transformer it is not connected... Is there an easy fix or do I need a transformer with a common...

Air conditioner common wire [ 2 Answers ]

I just installed a digital thermostat. The common wire does not seem to work. How can I get it to work?


View more questions Search