    Is Romex listed to be installed on the outside of sheetrock?
    I was inspecting a church recently and noticed that they had installed romex wiring into an existing light switch. It went from there about 20 feet to a light bulb. This was done to give light to an enclosed area under an egress stairway. Can Romex wiring be wired so that it is in front of the sheetrock? I've only seen it behind the sheetrock and in other voids during construction.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Feb 24, 2009, 09:21 AM

    You see it all of the time in basements and garages. However, every town has a building department and they can tell you if their codes allow this, likely not.
    fire inspector's Avatar
    fire inspector Posts: 5, Reputation: 1
    New Member
     
    #3

    Feb 24, 2009, 09:31 AM
    Quote Originally Posted by ballengerb1 View Post
    You see it all of the time in basements and garages. However, every town has a building department and they can tell you if their codes allow this, likely not.
    Yeah, I have already put in an email asking my counterpart over at the Bldg. Dept. what he thinks on it. Thanks for the reply.:rolleyes:
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Feb 24, 2009, 09:34 AM

    Do you know which code book your town has adopted and are there additional codes for this locale?
    fire inspector's Avatar
    fire inspector Posts: 5, Reputation: 1
    New Member
     
    #5

    Feb 24, 2009, 11:03 AM
    Yes, we use the ICC (International Code Council) codes. I was looking in NFPA 70 to see if they mention it, but had to locate the generic term for romex. It appears that it is called non-metallic flexible conduit.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Feb 24, 2009, 11:13 AM

    The generic term is NMB.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Feb 24, 2009, 12:52 PM
    The correct term is "Nonmetallic Sheathed Cable".

    NM cable, NMB, Romex, are all generic terms depending on where you are.

    NM cable can be installed exposed, as long as it is not subject to physical damage.

    See NEC 334.10 & 334.12
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #8

    Feb 24, 2009, 03:17 PM

    I don't believe NM is allowed in a church stairwell outside the sheetrock.

    334.12(A)(5) which covers a use not permitted for NM refers to 518.4(B). 518 covers assembly occupancies. Glancing through that article I see that NM is allowed only if installed in portions of the building not required to be of fire rated construction. I would have a hard time believing an egress stairway wouldn't be required to be of fire rated construction.
    fire inspector's Avatar
    fire inspector Posts: 5, Reputation: 1
    New Member
     
    #9

    Feb 24, 2009, 03:51 PM
    I agree. As the stairwell is a required path of egress, I believe that it would not be allowed to be exposed like this either.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #10

    Feb 24, 2009, 04:15 PM
    WHOA! I just realized. You said church.

    NO NM cable AT ALL Is allowed in a church. A church is a "place of assembly". NM cable is not allowed in a place of assembly except for certain specific instances.
    Must be MC cable or conduit with an insulated ground.
    fire inspector's Avatar
    fire inspector Posts: 5, Reputation: 1
    New Member
     
    #11

    Feb 24, 2009, 04:39 PM

    Yes. Exactly, a Place of Assembly. I'm also requiring them to have a licensed electrician send us a letter stating the installation meets current Code. And I'll probably ask the Bldg. Dept. Electrical Inspector to check it out as well.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Painting new sheetrock [ 2 Answers ]

I just finished drywalling my basement. What are my next steps for painting?

Allowable # of romex in a 2" romex connector [ 2 Answers ]

Hi, I would like to know the maxamum allowable romex wires can be secured in a 2" romex connector. Thanks

Can romex be installed in a conduit [ 13 Answers ]

I am installing a new 100A sub-panel. The feed will be from main with a 100A dual-pole breaker. The main and the sub-panel are in the basement. The new sub-pnael Will be about 25 feet from main. I already bought the feed cable for this sub-panel. I bought #4/3 With Ground NM-B romex. The...

Sheetrock around a gas fireplace [ 5 Answers ]

When framing around a fireplace a 1/2" space is needed all the way around the fireplace. At the top of the fireplace the gap is about 2" because the Quadrafire fireplace has some fins at the top (fins to the framing is 1/2", but firebox to framing is 2"). When I sheetrock around the fireplace, do...

Sheetrock [ 3 Answers ]

What is 'fire tape'? Can 'green board' be used on ceilings? What are the various coatings on nails and screws and what are their uses?


View more questions Search