    60 amp sub panal added to a 200 amp panal?
    I have a 200 amp panal in a new basement less then 5yrs old. Square D box.
    There is about 8 open spaces left. There is a dryer,oven/cook top,60 amp sub panal,
    And lots of 20 and 15 amp breakers. How do I figure if there is room in this box for another sub panal for the basement finish? When adding up the breakers now there is a total of 565 amps total now.
    Thanks for the help.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Feb 23, 2009, 08:15 PM
    The question is not do you have room for a sub-panel. A sub-panel does not draw anything. And you could fill it with 20A breakers that each feed one amp loads.

    The question is does your service have enough capacity for the basement re-model. A demand load calculation is the only way to tell this.

    Counting up the breaker is a meaningless number. It's like counting up the numbers on your car's speedometer.

    I will say, your 200A service will most likely be fine if you have that many open spaces still.
    What could you possibly add to a basement finish? 3-4 new circuits?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

Value added tax [ 2 Answers ]

Why The Rate Of Value Added Tax varies from state to state? / on what factors does it depend on Basically?

Grounding service enterance panal [ 1 Answers ]

The means for grounding a 200amp delta service enterance panal? The grounded and the grounding are on the same bus bar, Where should I ground my grounding rod & #6 bare grounding wire?

Run a 220 line from electrical panal to an outlet [ 3 Answers ]

I would like to run a 220 line from electrical panel Box to an outlet for a table saw.what for breakers And what gage wire should I use I will be about 20FT From panel? The saw motor is a 2hp 1 phase, runs at 3450 rpm And draws 10.2 amps

Breaker panal location [ 2 Answers ]

Hello, We are going to install wiring for our garage, so we are preping before the floor is poured. Today I need to dig a trench so we can put a sweep in to push our eletrical through at a later date. The electrical is buried and coiled up about 3 feet from the garage. Is there any codes...


View more questions Search