New Member
|
|
Feb 6, 2009, 02:36 AM
|
|
Pump head calculation farmaula
Send & explaine me pump head calculation farmaula
|
|
 |
New Member
|
|
Feb 11, 2009, 02:20 AM
|
|
Safdar,Your question is not explicit. You need to state what purpose you are applying the pump to serve. Is it a booster pump? Or a chilled water pump for HVAC?
The way we calculate the head for a chilled water pump in a closed system defers from the way we calculate for a booster pump in plumbing.
|
|
 |
Junior Member
|
|
Mar 16, 2009, 05:17 AM
|
|
The way to calculate pump heat:
In closed system: you add the pressure losses due to piping and all accessories with the piping such as elbows, valves, strainers etc. plus the pressure losses due to equipments
In short the pressure losses in the longest run of pipes in series with the piping.
In open system: same as the above plus residual pressure for the furthest fixure and cooling tower height difference (if any)
|
|
 |
New Member
|
|
Jun 7, 2009, 02:34 AM
|
|
In a closed circuit is it necessary to calculate the losses in yhe chilled water return lines.
Regards 1099
|
|
 |
New Member
|
|
Jun 7, 2009, 02:41 AM
|
|
Is it necessary to add up the friction losses in a return line of a closed circuit chilled water line?
Regards 1099
|
|
 |
New Member
|
|
Jun 7, 2009, 02:44 AM
|
|
Is it necessay to add up friction losses of water return lines in a closed chilled wter circuit?
|
|
 |
New Member
|
|
Jun 11, 2009, 03:14 AM
|
|
In a chilled water secondary system which has no of FCUs & AHUs do you have to consider pressure drop through the cooling coils of all the units?
|
|
 |
New Member
|
|
Jun 19, 2009, 04:49 AM
|
|
1099,
In a closed system, it is important that you add up all frictional losses due to pipe and fittings along return line while calcuting your pump head. Remember it is a closed system and the pump would have to push the chilled water through both supply and return lines, thus it must be able to overcome the frictional losses generated by their pipes,fittings and even the coil.
Ashiskg,
In a chilled water secondary system you must consider the pressure losses through the cooling coil of the AHUs and FCUs. Apparently, the cooling coils would pose some resistance to the flow of chilled water and this MUST be overcome by the pump head.
|
|
 |
New Member
|
|
Jun 19, 2009, 04:59 AM
|
|
During load estimation for an office block with indoor transformer and electrical panel rooms to be cooled, how can I get an idea of the heat dissipation from the equipments when it is not stated in their literature? Is there a guide from ASHRAE for these,as in, kw/sqm ?
|
|
 |
New Member
|
|
Jun 30, 2009, 01:36 AM
|
|
What is the function of the pressurization unit in chilled water system
|
|
 |
New Member
|
|
Jul 16, 2009, 12:48 AM
|
|
The pressurisation unit provides make up water in the chilled water pipes there is considerable loss of water while the pump are out operation and which it starts working there should be no losses in pressure for which it maintains the correct water level
|
|
 |
Junior Member
|
|
Aug 6, 2009, 04:41 AM
|
|
Hello All
1099: correct you have to count the return. It a loop.
Ashisskg: No, only one unit will be added to the friction, the unit that is in the longest loop
Ashnotcon: Transformer heat dissipation is 1.5% it's size in KW. Electrical Panel is 1.2% of its size in KW.
Omar: pressurization unit is used to cushion the expanded water in the pipes, so pipes do not burst. It also used to compensate pressure and add water to the system if the pressure in the system drops due to leaks or water getting colder.
Please rate me
|
|
 |
New Member
|
|
Sep 6, 2012, 11:05 PM
|
|
I need to calculate booster pump head for water supply
|
|
 |
New Member
|
|
Sep 6, 2012, 11:06 PM
|
|
I want to calculate booster pump head for water supply
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Pump head calculation
[ 1 Answers ]
Is there any book available to calculate hvac chiller pump head calculation and also pump head calculation for Cooling Tower Pump Head?
How to calculate hvac chiller pump head?
Cooling Tower Pump Head
1) Cold Water from Cooling Tower comes out with 150dia pipe and there are 4 x150dia pipes...
Pump head calculation
[ 0 Answers ]
Dear Madam / Sir
In our oil platform we have 3 gas turbines. The fuel for them is supplied by a sour,wet gas from a gas well. I would like to know,in terms of corrosion, which of the following options is desirable and technically accepted.
1- To heat the gas above its dew point in order to...
Pump head calculation
[ 2 Answers ]
Can some body make an effort to teach me pump head calculations. Thank u.
View more questions
Search
|