    Gibson furnace cycles different all the time
    Hi,I noticed my gibson furnace m#KG6RK 072C-12A S#KGA021204267 cycling an not starting. It locked out.got a flashing light said I had a bad ground.so I took it apart and found nuetral wire melted to flue and other wires melted to inducer.I clip out bad wires and reconnected and cleaned off flame senser.it seem to work fine for about a day then it would start on the 2nd try or third try or sometimes lock out again. I have a red(hot) wire coming in and a white (nue) wire coming in.I don't see a ground wire coming in.any suggestions on what to do from here.thanks,greg
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 7, 2009, 06:28 PM
    Here is your install manual. That furnace is branded by about 5 different names and Gibson is just one of them. There is a complete wiring and check out listed in this manual. The diagram clearly shows a need for a ground wire and I am surprised it worked at all without one.

    http://www.nordyne.com/Literature/a779a.pdf

    Install manual.

    http://www.nordyne.com/Literature/708291b.pdf
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #3

    Feb 8, 2009, 09:30 AM

    Thanks for the info, that will help plenty. Greg
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 8, 2009, 10:39 AM
    You will get it working again.
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #5

    Mar 7, 2009, 01:02 PM

    Hi,the furnace is grounded.I'm still having problems with it.I'm getting 4 flashes which is ignition failure,where should I go from here?thanks greg
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #6

    Mar 7, 2009, 01:32 PM

    The igniter had a resistance of 100 ohms,the roll out switches were 0 ohms, so I think there is nothing wrong there.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Mar 7, 2009, 01:37 PM
    i'm getting 4 flashes which is ignition failure,where should i go from here?thanks greg
    What does it say the 4 flashes indicate? Look in manual or on back side of blower acces door.

    What is the resistance supposed to be according to the manual for your unit I posted?
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #8

    Mar 8, 2009, 12:15 PM

    I don't think it gives me that information in the manual. Thanks greg
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Mar 8, 2009, 04:37 PM
    See this link below. Look for figure 28 on page 30. Now READ the lower left side information in regards to 4 Flashes. I posted this information above in my first post back to you. You should read ALL the links and information I posted here. I spent my time looking all that stuff up for you so the least you could do is read it. I also suggest you keep a copy of that information for future use on your computer and also in a safe spot like a CD or DVD. You may not find that information so easy again.

    http://www.nordyne.com/Literature/708291b.pdf
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #10

    Mar 10, 2009, 09:06 AM

    OK,somehow your not following me.I know what the 4 flashes stands for I even state what it is in one of my questions,it is ignition failure(check ground)i've checked the ground.now I would like to know where to go from here.I happened upon an answer you gave somebody about how much resistance a igniter should have,so I checked mine its 100 ohms.you stated for their igniter should be around 60-300 ohms,I was wondering what mine should be.trust me I've read the manual link you sent me but certainly can't find what the ohms should be for mine if even different which it probably isn't. The igniter may not even be an issue,but felt I should check it anyway.so anyhelp on trouble shooting my problem would be greatly appreciated. Thanks,greg
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #11

    Mar 10, 2009, 09:31 AM
    OK we need step by step from start to failure.

    If after reset you still are getting 4 flashes it is still indicates bad ground. I need to confirm this. You checked the ground wire from the main electric panel to the furnace disconnect then to the furnace ground? Is this correct?

    You checked that the circuit board has a good ground? Many times this ground is a wire OR the circuit board screws to the furrnace metal. Did you check this ground also?

    The reason is that the ground is a very important for these units and a bad or intermittent ground will cause problems that you will never figure out if the ground is bad. That is why the ground has to be confirmed GOOD all the way from the panel to the furnace and then to the circuit board.

    In your initial statement

    i have a red(hot) wire coming in and a white (nue) wire coming in.i don't see a ground wire coming in.any suggestions on what to do from here.thanks,greg

    You said you did not have a ground so this also bothered me as now you seem to have found one?

    Also any time you have had a short circuit like melting wires it can cause other problems down the road. We are dealing with sensitive electronics here.

    Also check to be sure the neutral wire is going to the neutral on the furnace and the power wire is going to the power wire on the furnace. You would not believe how many times a reversal of these two wires have caused problems. Sometimes they will work for awhile then fail until the wires are placed correctly.

    One last item. Post the exact chain of events from start up to failure. IE call for heat,inducer fan on,etc.
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #12

    Mar 13, 2009, 01:18 PM

    Hello,thanks for replying,I was checking to see if the hot & nue wires coming from the electric panel were hooked up right at the unit which they are, then the unit kicked on and I noticed that only one burner was lit. I've never seen it do that before.so I took out the burner assembly and blow it out with my air compresser.there was dust debris in between the burners keeping the gas from traveling from burner to burner.hence my problem.thanks again for your time and knowledge, I appreciate it. Greg
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #13

    Mar 13, 2009, 05:55 PM
    You have it going for now and that is good.
    Mikie D's Avatar
    Mikie D Posts: 45, Reputation: 1
    Junior Member
     
    #14

    Mar 14, 2009, 04:34 PM

    The flame sesor has a resistor wire did that melt to inducer and did you check pressure switch remember it is open when the system starts and then the inducer motor pulls in the pressure swith to make and then the system starts. Try jumping out pressure switch 5 seconds after inducer motor starts. Let us know Mikie D.
    frissbeegolfer's Avatar
    frissbeegolfer Posts: 16, Reputation: 1
    New Member
     
    #15

    Mar 15, 2009, 08:17 AM

    Its working now.thanks, greg
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #16

    Mar 15, 2009, 09:12 AM
    Glad you got it going Greg. If you have any more problems post back

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace Cycles Too Often [ 2 Answers ]

We recently replaced our old thermostat with a new Noma 5+1+1 thermostat. The furnace used to come on and run for a while, bringing the temperature to 1 degree higher than it was set for. Now it is set for 20.0 C and it comes on at 19.2 and goes off at 19.6. it doesn't even bring the temperature to...

Furnace cycles too frequently [ 1 Answers ]

I'm using a Honeywell Chronotemp IV Plus thermostat on my Trol-A-Temp system oil furnace. When the thermostat calls for heat, the furnace come on, all is well, and shortly thereafter the thermostat turns off its call for heat. The house maintains temperature fine. It's just that there is...

Furnace cycles on and off [ 10 Answers ]

I have a Heil PGAA24C1K1 natural gas furnace with a programmable thermostat, digital type. The unit cycles on and off frequently when heating, I've done a lot of searching but my problem is different that most others I read. First, this only happens when it's cold outside, like 25 degrees or...

Gas Furnace Repeatedly Cycles [ 2 Answers ]

I researched this in this help desk and got some good ideas, but none worked. It sounds similar to a dirty flame sensor. The furnace is forced air gas from mid-1980s. I do not see a manuf on the labeling, but there is a Honeywell control unit. If I remove the thermostat and just connect the...

Furnace heat cycles on/off [ 1 Answers ]

We have an old furnace,not quite sure how old.It is a Bryant Quietair.I noticed tonight the burners would light,stay lit for a few seconds(30-40secs.),then go out,and then relight a few seconds later.The fan is running throughout the whole process like it should.This goes on constantly.What is...


View more questions Search