    3phase generator for 110v system?
    I have the opportunity to buy a large 25KVA generator for a great deal. My dental office loses power a few times a year. Sometimes for an hour, sometimes a few. Never know whether to cancel the day's patients or wait for the power to come back on. My question: I have 3 separately metered 200amp panels in my building and would like to have them all covered by the generator. Most of my equipment is 110v with the possible exception of the compressor, vacuum system and heat pumps. I'm not sure to tell the truth. Before I have an electrician come out to eval this further, I thought I'd throw this out there. Here are the specs. Is this possible and/or reasonable? Thanks!

    Emergency Back up generator out of Bank.
    Propane fuel
    88 Total Hours
    Three Phase power 277/480 volts!! No single phase without using external transformer.
    Nice Panel/Tranfer Switch
    Starts and Runs like new, Exercised weekly.
    1.2L 4CYL motor large unit. Very industrial generator.
    Model# 95A 00530 S Generac
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Feb 2, 2009, 08:56 PM
    This is wrong on many levels.

    First off, you certainly can get single phase without a transformer. It would just be 277/480v single phase. Not very helpful I know.

    In my professional opinion, there is NO WAY it would be worth getting that thing. The installation and parts would be prohibitive with regard to any deal you might be getting on it.
    Do you know how much a 25kVA 480-240v step down transformer cost??

    You would also need a main transfer switch rated for the full service, which I assume is either 400 or 600 amps, and installed ahead of all the meters.
    Price up some gear with those ratings. That genny will not be looking so good.

    Sorry.
    srichdds's Avatar
    srichdds Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 3, 2009, 09:06 AM
    Quote Originally Posted by stanfortyman View Post
    This is wrong on many levels.

    First off, you certainly can get single phase without a transformer. It would just be 277/480v single phase. Not very helpful I know.

    In my professional opinion, there is NO WAY it would be worth getting that thing. The installation and parts would be prohibitive with regard to any deal you might be getting on it.
    Do you know how much a 25kVA 480-240v step down transformer cost???

    You would also need a main transfer switch rated for the full service, which I assume is either 400 or 600 amps, and installed ahead of all the meters.
    Price up some gear with those ratings. That genny will not be looking so good.

    Sorry.
    THANK YOU for saving me the time and grief. Appreciate it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

3phase over 1phase [ 3 Answers ]

What is the difference between 3phase over 1 phase system?

Wire a 3phase welder with 1phase power ? [ 2 Answers ]

Have heard this can be done but wanted to get some help. Have a three phase welder and wondered if I can directly wire a single phase line to it? I realize I would loose 66% of the out put which is fine but just wanted to know if it can be done. If so were do I put the single phase lines to? There...

Fitting 30ma circuit breakers to 3phase distri. Box [ 9 Answers ]

Hi, I am living in the South of France and the power supply to my house is 3 phase. The overall supply is 9kv giving a max of 3kv on each phase. I tried to fit a type AC 30ma breaker to each phase for safety reasons but have failed somewhere! The supply is 3 lives (220v each) and 1 neutral. I...

Trouble shooting a 3phase system [ 10 Answers ]

Hi All, I have a 480 VAC 3 phase ungrounded system. We monitor the system via a set of lights for each phase. If one phase goes to ground then that light should glow bright. In my case I have the B phase light out completely. While trouble shooting the problem I found which disconnect switch was...


View more questions Search