Ask Experts Questions for FREE Help !
Ask
    Noriel's Avatar
    Noriel Posts: 5, Reputation: 1
    New Member
     
    #1

    Jan 29, 2009, 09:20 PM
    Circuit breaker load
    I have 70 amp. Breaker, and has 2 unit /motors to be hooked up
    Combined load of motors 49 amps.?
    Nordic58's Avatar
    Nordic58 Posts: 3, Reputation: 1
    New Member
     
    #2

    Jan 29, 2009, 09:26 PM

    The breaker is intended to protect the wire which for 70amp would be #6. You can connect (2) loads to one breaker, as long as each of the loads is protected at their rating, usually done through a disconnect switch with fuses. Additionally the breaker should not be loaded more than 80% for a continious load (more than 3 hours) and for a motor load, should be sized 125% of the FLA.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jan 29, 2009, 09:43 PM
    Quote Originally Posted by Noriel View Post
    I have 70 amp. breaker,,and has 2 unit /motors to be hooked up
    combined load of motors 49 amps.??????
    Are you asking how this should be done? Or are you asking if it is OK?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jan 29, 2009, 09:43 PM
    Quote Originally Posted by Nordic58 View Post
    The breaker is intended to protect the wire which for 70amp would be #6.
    This would only be true for THHN conductors in conduit. #6NM cable is only good to 60A

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Maximum load on 20 amp circuit breaker [ 14 Answers ]

I am aware of certain normal maximums. I guess I'm looking for somebody to tell me that I'm pushing things too far, or not. I want to hook up a portable air conditioner (Sunpentown WA-1220E) which is rated at 950 watts (and, mysteriously, at 9.0 amps) along with an HP 4Si printer, which is rated...

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Calculating load per circuit breaker [ 3 Answers ]

How do I calculate how much load I can place on a nn amp circuit breaker? My knowns would be voltage and watts per hour. How to I allow for (amp draw) when a shop motor or freezer compressor spins up at initial start?

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...

Circuit breaker load [ 2 Answers ]

I'm remodeling my basement, & putting in a lot of elec'l outlets. Wondering how many outlets, or how do I figure how many, I can put on one ckt brkr. I'm using no. 14 Romex & 15 amp brkr. Tom :confused:


View more questions Search