    20amp outlet
    I am replacing all of the wiring in my old home. I am using a 20a breaker with 12-2 wiring. I'm pretty sure that I have to use 20a outlets and switches as well right? I ask because the 15a outlets and switches are less expensive. I am also confused because the 20a and 15a parts both opperate at the same voltage, but different amps.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 24, 2009, 05:43 PM
    Well, first off, voltage is not amperage, and vice-versa. Amperage is the size of the circuit.

    Unless you are in Canada, you CAN Use 15a receptacles on 20A circuits. The only exception is if you have only one receptacle. By this I mean one simplex receptacle. One standard duplex receptacle is two receptacles on one yoke.

    Switches are depended o the load. If the load you are switching is 15A or less then you can use 15A switches.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Changing 15Amp outlet to 20Amp [ 3 Answers ]

Recently had a generator installed for the business. Electrician mistakenly added 15amp power outlet within the generator housing unit. Need to change this to 20amp to plug in the block heater. My assumption is that the breaker is a 15amp breaker. If we change the outlet at the generator, will...

20amp QUAD double pole versus 2 20AMP tandem single pole [ 2 Answers ]

I have 5 zones of baseboard heat, 3 of which were disabled due to the addition of a heat pump. The circuit panel is full and would like to restore the operation of the 3 zones of base boardheat. I was planning on removing 3 double pole 20amp 240 volt circuits and installing 3 QUAD 20 amp double...

20amp plug with 30 amp outlet [ 4 Answers ]

I purchased a used tanning bed with a 220 plug and 20 amps.the outlet I am going to use is 220 volts and 30 amps.will this work , or will it damage something?

15amp or 20amp? [ 2 Answers ]

Does the 2005 NEC allow bedroom and living room outlets to be on a 15amp circuit? I am familiar with the 80% rule. Thanks in advance. Tom

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...